no EMT for outdoors???

An electrician just told me that code (southern California) no longer allows EMT conduit for outdoor use. It must be PVC. I asked him why they make waterproof EMT compression fittings. He said that's for indoor use in damp areas. True or not true?
 
  #2  
Old 08-15-07, 02:38 PM
Rollie73's Avatar
Member
Join Date: Mar 2007
Location: Bras D'Or, Nova Scotia ,Canada
Posts: 163
Upvotes: 0
Received 0 Upvotes on 0 Posts
True within Canada and many other places I have worked, however, the US guys will have to clarify the issue when it pertains to your area.
 
  #3  
Old 08-15-07, 04:03 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
it may be state or area specific but there is no restriction from using it outdoors in the NEC.
 
  #4  
Old 08-15-07, 04:11 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
They had changed the codes for compression fittings. They have to be listed rain tight now.
 
  #5  
Old 08-15-07, 06:55 PM
W
Member
Thread Starter
Join Date: Mar 2006
Location: United States
Posts: 123
Upvotes: 0
Received 1 Upvote on 1 Post
I bought the rain tight compression fittings. This is the first time I've heard EMT was not allowed outside. I wonder if this electrician is nuts. I can't imagine that of all the places in the U.S., EMT would be a no-no in a mostly desert environment (Southern California).
 
  #6  
Old 08-15-07, 06:59 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,262
Upvotes: 0
Received 0 Upvotes on 0 Posts
ANYTHING is possible in California when it comes to codes and laws.
 
  #7  
Old 08-15-07, 08:29 PM
H
Member
Join Date: Mar 2007
Location: Tustin
Posts: 85
Upvotes: 0
Received 0 Upvotes on 0 Posts
depends on the city, I know in anaheim, the raintite fittings must be listed for use by ul then the city tests and approves the ones you can use... stupid I know but after all this is so cal
 
  #8  
Old 08-15-07, 09:39 PM
D
ddr
ddr is offline
Member
Join Date: May 2006
Location: New York City
Posts: 126
Upvotes: 0
Received 0 Upvotes on 0 Posts
Like the others said, the NEC doesn’t have an issue with it , but your local code might. New York City code has added a subsection (7) to 358.12 that prohibits the use of EMT “For underground or exterior installations or in wet locations.”
 
  #9  
Old 08-17-07, 09:34 AM
W
Member
Thread Starter
Join Date: Mar 2006
Location: United States
Posts: 123
Upvotes: 0
Received 1 Upvote on 1 Post
Just a follow-up question. Is there a specific type of wire that must be used with outdoor EMT or PVC? The conduit will be attached to the outside wall of the house. I read that THWN may be used, but must it be used? Can I strip my leftover NM-B cable and use those wires? Thanks.
 
  #10  
Old 08-17-07, 09:54 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
Use THWN or dual rated THHN/THWN for outdoors in conduit. You may NOT use NM-B, even if you strip the outer jacket and just use the wire.
 
  #11  
Old 08-17-07, 12:40 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
> Can I strip my leftover NM-B cable and use those wires?

No. NM cable is rated and listed as an assembly; removing individual wires from the cable assembly voids the listing. The individual conductors are not listed for use. In addition to this, NM is only rated for indoor use so pulling the wires out for outdoor use would be improper anyway.
 
 