3~ Motor rating amps?
Old 08-21-07, 07:38 AM
I got an American 3-phase motor. It is labeled:
RPM: 1740 Hz: 60
V.: 208-240
F.L.A.: 8.8-9.2
S.L.A.: 9.6-10
What does the F.L.A tell?
and
What does the S.L.A tell?
Thank you!
Old 08-21-07, 09:11 AM
The FLA is the full load amps or the amperage the motor will draw if it is doing its rated horsepower worth of work.
Old 08-21-07, 09:14 AM
If I am not mistaken, F.L.A. is the Full load amps (current) and S.L.A. is the starting load amps. (The current ratings of the motor).
Old 08-21-07, 09:33 AM
Thank you!
Quit logic, when you tell me.
Then I can put on an motor protecting switch (thermic) rated to 9.2 amps.
Again
Thank you!
Old 08-21-07, 09:46 PM
Dsk ;
let me add one more thing to the list
add 25 % for O/L device
8.8-9.2 amp at 240 v 3 supply
set the O/L at 11.5 amp unless you have something that can be get jammed up for some reason then drop the OL a little
DSk i know you are in european area i just want to give you a gentle reminder to use the class C overload relays or sensors that will handle the common start up loading on the motors
thanks , Marc
i am sure you understand you may have to derate the motor a little due the differince in the HZ suppy you will only get 5/6 of the speed and also the 5/6 of hp rating as well
Old 08-21-07, 11:44 PM
One correction the S.L.A. is not the starting load amps it is the service load amps that the motor runs at when loaded at its service factor usually 1 to 1.15
roger
Old 08-22-07, 12:45 AM
Talking
Thank you again.
On the other side of the motor It is another plate;
50Hz
190-220V
F.L.A. 9.2-10.4
S.F.A 10-10.8
380-440V
F.L.A. 4.6-5.2
S.F.A 5-5.4
In Norway we have 2 systems: 3-phase 230V And 400V (both systems made to 230V single phase possible)
Then I can put on an adjustable motor protecting switch (thermic) rated to 4-6.3 amps.
for the 400 V system, or 10-16 amps for the 400V system.
These motor protecting switch es copes with 2-3 times the load for a start periode of a few seconds.
dsk