Generator Transfer switch
#1
Member
Thread Starter
Join Date: Jun 2007
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Generator Transfer switch
I'm building a new house and plan in installing a manual transfer switch for a generator. The switch will be 50amp and be located about 40 feet from the main panel. It will supply a 240v well pump and some small appliances and lighting. Everything will be inside the basement. What size wire do I need and should it be in a conduit?
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Whether or not the wire is in conduit depends on the type of wire used. A cable (NM or UF) does not need to be in conduit unless the conduit is for protection where the cable is exposed. Individual conductors need to be in conduit.
Use 8 gage wire.
What size is the generator you are using? You need a hefty generator for a well pump.
Use 8 gage wire.
What size is the generator you are using? You need a hefty generator for a well pump.
#3
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you plan on using NM, (romex) then you cannot use #8awg, you would have to use # 6awg....
But personally if this was my house I would install a 100amp transfer switch with a 24 ckt sub-panel... best bang for the buck...
But personally if this was my house I would install a 100amp transfer switch with a 24 ckt sub-panel... best bang for the buck...