What size wire
Old 08-23-07, 07:07 PM
bagoftools's Avatar
New Member
Cool What size wire
Hi,guys
What size wire should I be using to wire 4 recess lights on one switch and 4 sconses on another switch running to one circuit.The books I been reading say 14 but an electrican said 12 with a twenty amp circuit.please help don't what to take the ceiling down twice.I plan on using 60 watt bulbs.but would like to have it wired for the max of 90 watt.
Old 08-23-07, 07:12 PM
Rollie73's Avatar
Since this is only a lighting circuit, I would use 14. Even if you use 100 watt bulbs in all 8 fixture for a total of 800 watts, the draw is still under 7 amps. Well under what a 14 gauge wire and a 15 amp breaker can handle.
However, if you ever plan on extending this circuit to include some general purpose receptacles, then do yourself the favor go with a 20A and 12 gauge wire.
Old 08-23-07, 07:43 PM
bagoftools's Avatar
New Member
thank you for your reply. I,ll go with the 14
The wire size must match (or at least be the minimum) based on the breaker that controls the circuit. If you're tapping into a 15A circuit, you can use 14ga (or 12 ga, but there's really no need). If you're tapping into a 20A circuit, you MUST use 12ga.
If you're running a new circuit from the breaker box, you can use a 15A or 20A breaker.
15A breaker = 14ga wire
20A breaker = 12ga wire
Old 08-24-07, 07:31 PM
Rollie73's Avatar
I read this as he is installing a new circuit, but I could be wrong.
Definetly follow Zorfdt's advice if you are tapping into an existing 20 A circuit.