Air Compressor Wiring

Installing a new compressor 230/1 and was wondering if the FLA is 16 and the Manufacturer is calling for a 30 amp breaker is it ok to use 12/2?
 
Sponsored Links
  #2  
Old 08-28-07, 11:20 PM
Member
Join Date: Dec 2006
Location: orange county
Posts: 285
Exclamation

Nope. A 30 amp breaker must be matched up with at least 10 awg.
 
  #3  
Old 08-29-07, 01:59 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,378
Actually the answer is maybe. If the air compressor is hardwired to a single branch circuit then special rules apply. These rules are found in Article 430 of the NEC.

However, you cannot go wrong with the 30 ampere / # 10 wire rule.

This is also a moot point if the motor is cord & plug connected to a receptacle that could be used for some other purpose.
 
  #4  
Old 08-29-07, 08:53 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
The mimimum ampacity for conductors to a single motor is the Full-Load current X 125%.
You can select the conductor size based on this calculation.

Good Luck!!!!
 
  #5  
Old 08-29-07, 09:13 AM
Member
Join Date: Dec 2006
Location: orange county
Posts: 285
Smile

Guess I'll continue to start my few responses (even to the "seemingly" simple answers) with "I am a novice" (lol). I was certain however that I would place no-one in danger. Long live the pro's on this site. I learn sooo much everyday.
 
  #6  
Old 08-29-07, 11:46 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,335
Sidecutter,

If you're interesting in learning about breaker and conductor sizing for motor circuits, check out NEC article 430. Many of the standard sizing rules go out the window when it comes to dedicated motor circuits.

The viewer is a little clumsy, but you can view a free version of the codebook here:
http://www.nfpa.org/freecodes/free_access_document.asp?id=7005SB
 
  #7  
Old 08-29-07, 12:10 PM
Member
Thread Starter
Join Date: Nov 2002
Location: Mass
Posts: 151
Ok i was going to go with a outlet and cord so I better stick to the 10 gauge
 