Romex Sheath Damaged

I found a cable that is damaged when I opened the floor between the second and first stories of my house. The outer white sheath of the cable has a small tear. There is a black sheath showing from one of the wires inside. No copper is exposed. Should I wrap this with tape? Is there a specific product to use?
 
Sponsored Links
  #2  
Old 09-18-07, 05:49 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Technically the cable needs to be replace, or a permanently accessible junction box used.

However, most people would probably go the route you are suggesting, using electrical tape..
 
  #3  
Old 09-18-07, 06:07 PM
R
Member
Thread Starter
Join Date: Jul 2007
Location: United States
Posts: 112
Received 0 Votes on 0 Posts
Thanks. The damage is so minor I think taping will be good enough.
 
  #4  
Old 09-18-07, 06:44 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Received 0 Votes on 0 Posts
If only the outer sheath is torn taping with electrical tape is a legal and safe fix. This is assuming the tear is not extreme.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: