Furnace wiring + condensate pump
Old 09-22-07, 01:46 PM
JoeTheZombie's Avatar
My furnace specifies a maximum 15A circuit. The wiring from the panel is 12/2, and the breaker is 15A. I have a small (2A) condensate pump I wish to install. I would like to:
Change the 15A breaker to a 20A, install a receptacle in the furnace closet for the condensate pump, and install a 15A fused disconnect for the furnace with power from the receptacle.
This would keep the furnace on a max 15A, and also supply power for my condensate pump.
Old 09-22-07, 02:31 PM
How many amps does your furnace need? Are you sure you need to go to all this trouble?
Old 09-22-07, 02:45 PM
The furnace ampacity is listed as 13.4A, and the max fuse or breaker must be 15A as indicated on the unit.
I need to install an outlet for the condensate pump, and doing it this way would let me use the existing wiring to the furnace rather than running a new circuit.
I read somewhere the NEC requires the furnace to be on a dedicated circuit, so that is where my concern stems.
Old 09-25-07, 10:15 AM
P
Convert the existing 20 amp Branch - Circuit to a "Feeder" by terminating the 12/2 conductors on the lugs of a 2-circuit panel .
DO NOT connect the EGC of the 12/2 cable to ANY Neutral terminations -- Bond a lug to the metallic surface of the enclosure , and connect all cable EGC's to the lug which "Bonds" together the enclosure and the EGc's .
Old 09-25-07, 10:53 AM
Z
Received 54 Votes on 51 Posts
I'd suggest tapping power from some other circuit nearby (basement lights, garage receptacle, etc) as the condensate pump is generally quite a low draw. That way you don't have to worry about additional fuses or panels or such. Just install a simplex receptacle (non-GFI in my opinion) and have at it.
Just my suggestion.
Old 09-25-07, 11:06 AM
Ed Imeduc's Avatar
Wink
Might check code there. lot of codes now call for a dedicated circuit to the furnace. With a cut off switch at the top of the stairs to the basement.