Sub Panel Finally!

Well it's that time. I finally get to install my sub in the garage (attached).

Main panel is 200 amp. Planning on installing 100 amp double pole breaker in it and running 2-2-2-4 ser al cable to sub panel which happens to be old mainpanel. I have to install a ground bar in this panel as it never had one.

Anyone see a problem with this configuration?

Cable will be within structure for the entire run.
 
Sponsored Links
  #2  
Old 10-01-07, 10:07 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Yes the grounding bar must be installed and also make sure the bonding screw/ band must be removed from the netrual bussbar but i am hope you are saying the SER this is for indoor useage cant run this outdoor at all

Merci, Marc
 
  #3  
Old 10-02-07, 07:05 AM
Member
Thread Starter
Join Date: Nov 2002
Location: Mass
Posts: 151
Originally Posted by french277V View Post
Yes the grounding bar must be installed and also make sure the bonding screw/ band must be removed from the netrual bussbar but i am hope you are saying the SER this is for indoor useage cant run this outdoor at all

Merci, Marc

I think the cabel is service entry rated (round) it will be indoors the whole run is this ok?
 
  #4  
Old 10-02-07, 09:03 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,530
Yes, SER is okay indoors. Be sure to use no-ox grease on the aluminum terminations.
 
  #5  
Old 10-02-07, 10:38 AM
Member
Thread Starter
Join Date: Nov 2002
Location: Mass
Posts: 151
Thanks will do.
 