Outdoor hot tub GFCI question

I've been reading that I need a GFCI breaker in the main panel and a cut-off switch outside for my hot tub. The hot tub cut-off switches for sale at Home Depot look like they include a GFCI breaker. So, can I use one of these and put a regular 50A breaker in the main panel?

~Brent
 
Sponsored Links
  #2  
Old 10-04-07, 02:27 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Yes, the GFCI disconnect satisfies both requirements for GFCI protection and maintenance disconnect. There are many other concerns when installing a spa; pay particular attention to the legal wiring methods for spas as well as the bonding requirements.
 
  #3  
Old 10-04-07, 04:02 PM
Member
Thread Starter
Join Date: Oct 2007
Location: us
Posts: 36
Received 0 Votes on 0 Posts
Thanks for the quick response.

I know I need to use a 8' ground rod and I need to ground the wire mesh used to reinforce the concrete slab. Am I correct that the mesh would also have to be bonded to the pump and controller box?

For the wiring, I know it needs to be 6awg. Should I run this in conduit all the way to the hot tub (underground). If so what type of conduit is best? It is about 25' total from the main panel to the hot tub. Cut-off switch would be about 6' from the tub. The tub is 240v/50A.

Thanks again,
Brent
 
  #4  
Old 10-04-07, 04:15 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
You do not use a ground rod. None. Period.
 
  #5  
Old 10-04-07, 07:51 PM
Member
Thread Starter
Join Date: Oct 2007
Location: us
Posts: 36
Received 0 Votes on 0 Posts
Originally Posted by racraft View Post
You do not use a ground rod. None. Period.
The spa manual says:

"Without proper grounding and bonding, a system malfunction may cause fatal shock"

..and..

"An approved ground may be an 8' long ground rod, a plate electrode, or a buried metal water pipe with at least 10 feet of buried pipe."

So you are saying I should only connect it to the ground from the house and not to a ground rod?

~BR
 
  #6  
Old 10-04-07, 08:07 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
The instructions are incorrect. Note that they are ambiguous. The word may is used...

You run an insulated ground wire out to the GFCI disconnect. From there a ground is run to the hot tub. All metal is then properly bonded.

No ground rod is used. No electrode. Nothing.
 
  #7  
Old 10-04-07, 11:04 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Originally Posted by rade0041 View Post
Thanks for the quick response.

I know I need to use a 8' ground rod and I need to ground the wire mesh used to reinforce the concrete slab. Am I correct that the mesh would also have to be bonded to the pump and controller box?

Thanks again,
Brent
not for hot tub useage as what Racraft saying with this word
You run an insulated ground wire out to the GFCI disconnect. From there a ground is run to the hot tub. All metal is then properly bonded
and
No ground rod is used. No electrode. Nothing.
that it.

Merci, Marc
 
  #8  
Old 10-05-07, 09:11 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by rade0041 View Post
Am I correct that the mesh would also have to be bonded to the pump and controller box?
Some local inspectors require bonding of the rebar mesh, others do not; check with your inspector on this one.

For the wiring, I know it needs to be 6awg. Should I run this in conduit all the way to the hot tub (underground). If so what type of conduit is best?
Use 1" or 1-1/4" PVC conduit buried at least 18" deep for the underground portions. For a pure 240V tub, you'll use two black #6 THWN hot conductors plus a #10 green insulated ground. For a 240/120V tub, you'll need to add a white #6 THWN neutral conductor. Some tub instructions require an upsize of the ground from #10 to #8.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: