subpanel circuit question

Reply

  #1  
Old 10-11-07, 10:36 AM
Member
Thread Starter
Join Date: Sep 2007
Posts: 35
subpanel circuit question

I just installed a Cutler-Hammer "load center" between the studs in my detached garage. The 6 ga (protected by a 60 amp breaker) subfeeds enter the bottom of the panel through conduit. The instructions that came with the panel show the circuits come out of the panel through the same side as the subfeeds. Is it permissible to use either the top or bottom of the panel for the circuits or must I use the bottom for the circuit wiring?
 
Sponsored Links
  #2  
Old 10-11-07, 10:48 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,539
You may use any combination of the knockouts for branch circuits: top, side, bottom, back.
 