Do I need a GFI for a dedicated sump

Reply

  #1  
Old 10-12-07, 07:31 AM
New Member
Thread Starter
Join Date: Jul 2003
Location: California
Posts: 27
Do I need a GFI for a dedicated sump

I ran a dedicated circuit to a sump pump for a small granny flat waste stream. Does this circuit need to be on a GFI? The receptacle and pump are on the exterior of the dwelling.

Thanks

Tom
 
Sponsored Links
  #2  
Old 10-12-07, 07:46 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,533
No GFCI protection is required if you use a simplex receptacle, however a weather tight box and in-use bubble cover is required for the receptacle.
 
  #3  
Old 10-12-07, 08:54 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
I'm going to disagree with Ben. There are such exceptions for basements and garages and outdoor ice-melting equipment, but not for this. GFCI is required.
 
  #4  
Old 10-12-07, 09:01 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
I don't think I would put a sump pump outdoors without GFCI protection. Even on a simplex receptacle. I think some inspectors might allow it, but I think it is (according to the letter of the code) required.

John, where have you heard of ice melting equipment exempted from the GFCI requirement? I looked ate several different products, and they all stated that GFCI protection was required. One even went so far as to provide it in their cord ands plug assembly.
 
  #5  
Old 10-12-07, 09:07 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
I didn't give all the conditions of the exemption. It requires certain construction of the equipment to qualify.
 
  #6  
Old 10-12-07, 05:55 PM
Unclediezel's Avatar
Member
Join Date: Dec 2006
Location: Northeastern PA.
Posts: 2,230
Wouldnt this require GFCI , By virtue of being an "OUTDOOR" receptacle????
 
  #7  
Old 10-12-07, 06:23 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Originally Posted by tola View Post
I ran a dedicated circuit to a sump pump for a small granny flat waste stream. Does this circuit need to be on a GFI? The receptacle and pump are on the exterior of the dwelling.

Thanks

Tom
Unforteally the code is very spefically on outdoor recepetale are mantory GFCI and i dont think they have any exempt on this part at all
 