Hello, I'm filling out my permit for new service to my garage 150amp 2/0 Alum.SEU and there's a part on the permit form I'm unsure of how to fill out. (I live in City) See (E2)below

E. ELECTRICAL WORK
SERVICE INFOMATION
E1. is for temporary service info... (no not doing)

E2. Perm.Service:Serv.Cond(Ohio)_____or Lateral(UG)______
10 No.Sets____Size_______Amps______
10 Serv.Sw_____No.Meters______ Volts_____
30 No Sets______Size______ Amps_______
30 Serv.Sw_____ No.Meters_____ Volts_____
Estimated Fault Current at Service Line Terminals_______
 
Sponsored Links
  #2  
Old 10-16-07, 02:11 PM
HotxxxxxxxOKC's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2006
Location: USA
Posts: 8,044
Usually licensed electricians have to fill these out, and most locales require this.

Is this a subpanel or a new meter service?
 
  #3  
Old 10-16-07, 02:18 PM
Member
Thread Starter
Join Date: Oct 2007
Posts: 17
It's a new meter box... I called the inspection place and they said either myself or electrician could fill form out. I noticed to there's no specific place for a electricians license# where as on other forms I looked up do have form boxes specific for electricians only. I have a copy of the forms scanned if you'd like to see it in full,might help.
 
  #4  
Old 10-16-07, 02:41 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Originally Posted by jsg007 View Post
Hello, I'm filling out my permit for new service to my garage 150amp 2/0 Alum.SEU and there's a part on the permit form I'm unsure of how to fill out. (I live in City) See (E2)below

E. ELECTRICAL WORK
SERVICE INFOMATION
E1. is for temporary service info... (no not doing)

E2. Perm.Service:Serv.Cond(Ohio)_____or Lateral(UG)______
10 No.Sets____Size_______Amps______
10 Serv.Sw_____No.Meters______ Volts_____
30 No Sets______Size______ Amps_______
30 Serv.Sw_____ No.Meters_____ Volts_____
Estimated Fault Current at Service Line Terminals_______

ok i can decode this for you

the 10 really mean 1 service
Cond (OH )mean overhead service drop cable size
lateral mean underground
Perm service just make a check mark depending on if you are overhead or underground cable
No.sets mean numbers of cables that will asked for paralled cable [ very rare for this but for now just wirte 1 ]

size mean the wire size in the meter box like 3/0 or #3 it depending on what you will install in there and make a note say CU or AL [ CU for copper AL for alum.]

Amps = size of main breaker either 100. 150 or 200

Service switch some case some area required a main switch before meter [ i doubt that but check out the POCO regulations for that ]

No.meters = numbers of electric meter will be in that place majorty of resdentail area useally is 1 but some case have 2 if dual rate meter for waterheater or specal useage

volts just type in 120/240 [ very common resdentail voltage unless poco say something diffrent like 208/120 that diffrent story ]

For the 30 = 3 just leave that part blank you dont need that
the last line the estamed falut current at line termails

this useally either 10 K or 22 K [ poco can tell you this ]


Hope this will help ya with the info

Merci, Marc
 
  #5  
Old 10-16-07, 02:59 PM
Member
Thread Starter
Join Date: Oct 2007
Posts: 17
Thankyou!!! I didn't expect such a good answ so quick, so I'll leave the Serv.Sw blank for now and fault current I think would be 22 since live close to power station..etc versus living outin country...at least from what I've read. Sure appreciate!
 