Can someone check my lighting calcs?

Reply

  #1  
Old 10-20-07, 11:00 PM
Member
Thread Starter
Join Date: Jun 2007
Location: Ludlow, MA
Posts: 172
Can someone check my lighting calcs?

I am going to run a lighting circuit in a garage. The lights are going to be 4ft 2 lamp shop lights on switched receptacles. Correct me if I'm wrong, but if I remeber correctly, these lamps are 32 to 40 watts. We'll say 80 watts per fixture?

A 14 guage, 120v, 15 amp circuit gives me 1800 watts to play with. Derating the lighting load (continuous duty) gives me 1440watts. This gives me a maximum of 18 four foot, 2 lamp fixtures, correct?
 
Sponsored Links
  #2  
Old 10-21-07, 06:20 AM
Rollie73's Avatar
Member
Join Date: Mar 2007
Location: Bras D'Or, Nova Scotia ,Canada
Posts: 173
I'm not sure about this rule in the US, but in Canada, you can only load the breaker to 80% capacity. This means you cant put 1800 watts on that 15A breaker. You can only load it to 12A or 1440 watts.


So to answer your question, YES, 1440 is the max you could load on the circuit. Be careful when considering this circuit, you may want room for future expansion. If the material is not already purchased and/or installed, do yourself a favor and run 12 guage and use a 20A circuit.
 
  #3  
Old 10-21-07, 12:30 PM
Member
Thread Starter
Join Date: Jun 2007
Location: Ludlow, MA
Posts: 172
I've got 20 amp circuits for the receptacles. I just wanted to make sure i didn't make a mistake. 18 shop lights seems like alot for a 14 gauge wire, but I think its right. I am a big fan of running 12 gauge too, but there is no way i am going to use even 10 lights on this circuit.

I think around here you're aloud to use 100% of the breaker, but for continuos loads, which lighting is considered, you derate to 80 percent.
 
  #4  
Old 10-21-07, 12:37 PM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
You can double the wattage-capacity by simply adding a 3rd conductor to the circuit.

Using cable?--- "14/3" or "12/3"

Tubing/Conduit ? --- Black/Red/ White conductors

Also , you can have 2 switches if you chose.
 
  #5  
Old 10-21-07, 01:06 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Yes, strider, your calculations are correct.

Most U.S. inspectors do not consider residential lighting as a continuous load.
 
  #6  
Old 10-22-07, 06:27 PM
Rollie73's Avatar
Member
Join Date: Mar 2007
Location: Bras D'Or, Nova Scotia ,Canada
Posts: 173
Thanx for the clarification on the code issue John. The only things I know about the NEC is what I'm learning on here. The CEC (Canadian Electrical Code) is a different story.
 
  #7  
Old 10-22-07, 07:14 PM
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,623
Your calcs work this time, but you should not use lamp wattage. You should use ballast wattage for load calcs.
 
  #8  
Old 10-23-07, 12:15 PM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
"Wattage" , or "volt-amperes" for Branch-Circuit calculations with ballasts?
 
  #9  
Old 10-24-07, 06:21 AM
Member
Thread Starter
Join Date: Jun 2007
Location: Ludlow, MA
Posts: 172
Do switched lighting receptacles in a detached garage have to be gfci protected? I assume they do.
 
  #10  
Old 10-24-07, 06:40 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
The term receptacles in your post is confusing.

Hardwired lights in a detached garage do not need GFCI protection.

Lights plugged into a receptacle would need GFCI protection if the receptacle were readily accessible. For example, a receptacle in the ceiling for a plug in fluorescent light would not need GFCI protection. A receptacle on the wall at normal height that a floor lamp was plugged into would need GFCI protection.
 