i just need to know which wire and breaker is for the 20 amp 240 volt plug in garage heater I need to finish my instulation

#2
You seem to have started in the middle of the question. Start at the beginning. Is it a detached or attached garage? If detached does it already have power going to it. What have you done so far? What type of electric heater?
#3
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,970
Received 0 Votes
on
0 Posts
A 20 amp circuit needs 12 gage wire. You might want to go larger size (smaller gage) if the run from the breaker is long.
You answered your own question about the breaker when you stated that the need is for 240 volts.