100 amp wire gauge

im running an exterior wire from my home to my garage undergound,the run will be about 65 feet.this wire will need to carry 100 amps,which gauge is recommended for this?thanks.
 
Sponsored Links
  #2  
Old 11-16-07, 10:10 PM
mukansamonkey's Avatar
Member
Join Date: Nov 2007
Location: Indianapolis
Posts: 120
Received 0 Votes on 0 Posts
At 65 feet you don't need to oversize for distance, so your hots and neutral should be run in #1 AWG copper. The ground wire is #8. Oversizing will only help if you plan to have very heavy loads running for extended periods of time, over time heavier wire will save a bit of power usage.
 
  #3  
Old 11-16-07, 10:25 PM
Member
Join Date: Oct 2007
Location: Delray Beach, FL
Posts: 406
Received 0 Votes on 0 Posts
Don't foget about grounding requirements at seperate structures.
 
  #4  
Old 11-16-07, 10:37 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
Just to be sure:
when you said "outside wire" did you mean to infer a direct buried cable? or simply that it was outside?

The #1 is the size if you are using UF. If you use other types of wire, the size may very well be different.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: