Is there anything in the NEC that speaks to how many wires can go under one screw on the grounding bar or if white and ground can be under the same screw?
 
  #2  
Old 11-21-07, 10:49 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Received 15 Votes on 13 Posts
One wire under screws in fixtures. Bottom line in panels is manufacturers instructions but generally one neutral wire only but two ground wires are ok.
 
  #3  
Old 11-21-07, 11:21 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 45 Votes on 43 Posts
The only rule specifically in the NEC is that neutral (white) wires must be one-wire-per-screw, no exceptions. Ground wires of the same gauge may be doubled or tripled per screw depending on the panel manufacturer's instructions on the panel label.
 
 