what size wire from house to shop?
I am in the process of gathering materials for wriing my shop. Its a 30x50x12 and its close to 200' from the house. I have purchased a 125 amp breaker panel for it and have set 20 some odd 20 amp outlets around the shop. I'll have 10 2 bulb (4') fluorescent fixtures and 2 2 bulb (8') flourescents for lighting. I bought a big roll of 12-2 for all the outlets and lighting.
I'll have a grinder, a table saw, an air compressor, a 2 post lift and typical other shop tools but I dont expect too many of them to be on at the same time. I will eventually get some sort of heaters in ther and if its not a woodburning stove, it will probably be electric (maybe a heat pump or strips). I also have a lincoln 225 welder and plan on getting a mig somewhere down the road.
Not having a clue as to power requirements for those items listed above, I cant really tell how much power I'll need and more importantly, since I am ready to buy wire to connect the shop to the house 200' away, I dont know what size wire to buy.
what size wire do I need? I see some online calculators that say 3/0 is the min and I see other posts that say I could get away with 2/0 or even 1/0. I dont want to undersize it at all or oversize it too much
Can anyone with experience help me out?
I'll have a grinder, a table saw, an air compressor, a 2 post lift and typical other shop tools but I dont expect too many of them to be on at the same time. I will eventually get some sort of heaters in ther and if its not a woodburning stove, it will probably be electric (maybe a heat pump or strips). I also have a lincoln 225 welder and plan on getting a mig somewhere down the road.
Not having a clue as to power requirements for those items listed above, I cant really tell how much power I'll need and more importantly, since I am ready to buy wire to connect the shop to the house 200' away, I dont know what size wire to buy.
what size wire do I need? I see some online calculators that say 3/0 is the min and I see other posts that say I could get away with 2/0 or even 1/0. I dont want to undersize it at all or oversize it too much
Can anyone with experience help me out?
#4
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Did I read that right, a 1,500 square foot shop? My whole house is only a bit over 1,500 square feet.
I am assuming that this is in an area that is zoned for residential and that you have no intention of using the shop space for any commercial purposes, right?
If it is only going to be you and maybe an occasional friend working in this shop at any one time then your electrical requirements will probably not be excessive. You have to allow for your lighting, air compressor (since it will be automatically starting) and the largest power tools / welder in use at one time. This would be your continuous (not in code terms) draw and then you add to this the starting draw of the largest motor. This calculation gives you the highest expected load and it is from this that you calculate the voltage drop over the 200 foot distance and calculate the necessary size of wire.
If this calculation gives you a lower sized wire than does the calculation for a 100 ampere feeder from the house then you use the proper size wire for the supplying circuit breaker (100 amperes) to the shop. If the voltage drop calculation shows a larger size wire is necessary to maintain the voltage drop to an acceptable level then you use the larger wire.
I would strongly urge you to NOT consider the use of electric heat in this shop because it will vastly increase your electrical needs. In all probability it would require no less than a 200 ampere feeder to the garage with allowance made for voltage drop AND a subsequent upsizing of the service at the house.
I am assuming that this is in an area that is zoned for residential and that you have no intention of using the shop space for any commercial purposes, right?
If it is only going to be you and maybe an occasional friend working in this shop at any one time then your electrical requirements will probably not be excessive. You have to allow for your lighting, air compressor (since it will be automatically starting) and the largest power tools / welder in use at one time. This would be your continuous (not in code terms) draw and then you add to this the starting draw of the largest motor. This calculation gives you the highest expected load and it is from this that you calculate the voltage drop over the 200 foot distance and calculate the necessary size of wire.
If this calculation gives you a lower sized wire than does the calculation for a 100 ampere feeder from the house then you use the proper size wire for the supplying circuit breaker (100 amperes) to the shop. If the voltage drop calculation shows a larger size wire is necessary to maintain the voltage drop to an acceptable level then you use the larger wire.
I would strongly urge you to NOT consider the use of electric heat in this shop because it will vastly increase your electrical needs. In all probability it would require no less than a 200 ampere feeder to the garage with allowance made for voltage drop AND a subsequent upsizing of the service at the house.
#5
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
yes, this shop is just for me to putz around in (no commercial stuff going on).
I have an old muscle car that i will be playing with and needed some room to put it and my truck. Since I had the land and the labor to build it, I went as big as I could afford (its taking a while to finish).
Anyways, i am undecided between running wire from my house out to the shop or just having another meter placed out there with an overhead service line. The meter and overhead line would just cost me the monthly service fee ($15 a month if I use no electricity and the service fee goes down from there- but the electricity is added to it). with the price of the wire, $930 for 500' of 1/0, I could put a meter in and cross over in about 7 years.
One of my biggest factoirs is that I dont want line drop and I really dont want to dig a 200' 24" deep trench in my rocky soil (it is on top of a hill so its pretty rocky). If I needed 2/0 or 3/0, the price of the cable goes goes up (not sure how much as I havent found a price for it yet) and the overhead line starts looking better- plus, with the overhead line I do not have to worry about maintenance or repairs if the underground gets damaged
I have an old muscle car that i will be playing with and needed some room to put it and my truck. Since I had the land and the labor to build it, I went as big as I could afford (its taking a while to finish).
Anyways, i am undecided between running wire from my house out to the shop or just having another meter placed out there with an overhead service line. The meter and overhead line would just cost me the monthly service fee ($15 a month if I use no electricity and the service fee goes down from there- but the electricity is added to it). with the price of the wire, $930 for 500' of 1/0, I could put a meter in and cross over in about 7 years.
One of my biggest factoirs is that I dont want line drop and I really dont want to dig a 200' 24" deep trench in my rocky soil (it is on top of a hill so its pretty rocky). If I needed 2/0 or 3/0, the price of the cable goes goes up (not sure how much as I havent found a price for it yet) and the overhead line starts looking better- plus, with the overhead line I do not have to worry about maintenance or repairs if the underground gets damaged
#6
I would really lean toward having a second meter installed to the shop. First, I don't think that you have enough capacity with you existing 100A service to add this shop in addition to your house. This would require a service upgrade at the house which would probably be around $1,500. Second, the cost of the wire for a 200' underground will be pretty substantial compared to the meter fee from the power company.
#7
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The power company says i have 200 amp service to the house. Thats 200 amps to the meter base. off the meter, there is a 100 amp breaker panel that feeds the house.
I was told I could run a separate panel coming off the the meter base (separate from the house panel) to run thru 100 amp breakers out to the shop. In the shop, I'll have the 125 amp breaker panel that has a 50 amp, a 30 amp and 6 20 amp breakers in it (no main breaker).
using various online calculators, it looks like I would need #1 or 1/0 THHN wire (and a #6 ground) from the house to the shop
I was told I could run a separate panel coming off the the meter base (separate from the house panel) to run thru 100 amp breakers out to the shop. In the shop, I'll have the 125 amp breaker panel that has a 50 amp, a 30 amp and 6 20 amp breakers in it (no main breaker).
using various online calculators, it looks like I would need #1 or 1/0 THHN wire (and a #6 ground) from the house to the shop
#8
I was told I could run a separate panel coming off the the meter base (separate from the house panel) to run thru 100 amp breakers out to the shop.
In the shop, I'll have the 125 amp breaker panel that has a 50 amp, a 30 amp and 6 20 amp breakers in it (no main breaker).
it looks like I would need #1 or 1/0 THHN wire (and a #6 ground) from the house to the shop
If you use THHN, you'll also need conduit. A direct burial aluminum cable such as USE (underground service) or MHF (mobile home feeder) may be a good option for you also. It's usually quite a bit cheaper than conduit and THHN.
#9
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Does your meter also have a 200A main panel attached in a meter/main combo? Do you know if your meter base is double lugged?
A main breaker will be required for this panel.
The minimum size wire you can use is #4-4-4-8 copper or #2-2-2-6 aluminum based on table 310.15(b)(6). Either of these provides about 5% voltage drop at maximum load. Code does not require you to upsize wires for voltage drop, but you might want to get to 3% which is the standard design goal. Using #2-2-2-6 copper or #1/0-1/0-1/0-4 aluminum achieves that goal. You could also use #1-1-1-4 aluminum to save a little cash which yields 3.6% voltage drop at max load -- certainly close enough to acceptable limits.
If you use THHN, you'll also need conduit. A direct burial aluminum cable such as USE (underground service) or MHF (mobile home feeder) may be a good option for you also. It's usually quite a bit cheaper than conduit and THHN.
#10
You may also want to consider installing a second conduit for low voltage wires if you ever want telephone, computer, cable TV or security system out at the shop. If you dig a 24" trench, put power at the bottom, backfill 12", then install the low voltage conduit and fill to grade. One trench, two conduits with 1 foot separation.
the meter has a panel attached to it but that panel has a 100Amp breaker in it with all the house's breakers. As for the meter base being double lugged, I am not sure.
I didnt know this. I thought the main breaker could be at the house only.
How do you come up with those gauges?
You've gotta be careful using online calculators. They often only size for just voltage drop or just NEC tables, but not both. You need to consider both requirements in determining the final gauge.
I initially believed I needed the 1/0 wire and I couldnt find any undergroung service type wire in that size.
#11
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
so seeing as this is going out 200' from the house meter, using #1 wouldnt be too small but, would actually be a size or 2 bigger than code, right?
Does #1 come in a 3 or 4 wire cable (an all in one)? I'd like to be able to talk somewhat intelligently to the guy at the electrical supply store.
Also, I betcha that I will have to change out my meter base to get the double lugs. Would there be a model number or anything like that on the one on my house where I can look up what it has? or is the only way to tell to have Entergy come out and pull the meter and actually look at it?
Does #1 come in a 3 or 4 wire cable (an all in one)? I'd like to be able to talk somewhat intelligently to the guy at the electrical supply store.
Also, I betcha that I will have to change out my meter base to get the double lugs. Would there be a model number or anything like that on the one on my house where I can look up what it has? or is the only way to tell to have Entergy come out and pull the meter and actually look at it?
#12
Does #1 come in a 3 or 4 wire cable (an all in one)?
Also, I betcha that I will have to change out my meter base to get the double lugs.
Would there be a model number or anything like that on the one on my house where I can look up what it has? or is the only way to tell to have Entergy come out and pull the meter and actually look at it?
#14
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thanks for the replies.
I was totally in the dark when I began this hunt for information and you guys really helped out a lot.
I was confused about the neutral wire too as I kept thinking it was the same as the ground (and therefore I was initially going to get #6 for the neutral). But Im thinking thats not true and that the neutral should be the same size as the hots. Should the neutral be the same size as the hots (ie, #1 wire for the neutral as well?). I know the ground wire can be smaller and I was going to use #6 for the ground.
On a side note, i looeked at the breaker panel for the house and it is actually a 150 amp panel and not 100 amp as I initially stated.
The meter base has no markings on it at all but it looks like the original one installed when the house was built in 1985. I'll call the supply house today about the meter base.
thanks again. Im am learning a lot through all this!
I was totally in the dark when I began this hunt for information and you guys really helped out a lot.
I was confused about the neutral wire too as I kept thinking it was the same as the ground (and therefore I was initially going to get #6 for the neutral). But Im thinking thats not true and that the neutral should be the same size as the hots. Should the neutral be the same size as the hots (ie, #1 wire for the neutral as well?). I know the ground wire can be smaller and I was going to use #6 for the ground.
On a side note, i looeked at the breaker panel for the house and it is actually a 150 amp panel and not 100 amp as I initially stated.
The meter base has no markings on it at all but it looks like the original one installed when the house was built in 1985. I'll call the supply house today about the meter base.
thanks again. Im am learning a lot through all this!
#15
I know the ground wire can be smaller and I was going to use #6 for the ground.
the house and it is actually a 150 amp panel and not 100 amp as I initially stated.
You would need to upgrade the 150A panel at the house to a 200A panel, then install the shop panel as a 100A subpanel off the new 200A main.
#16
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
That would be a problem for double lugging the meter. If your house is 150A and your shop is 100A, that puts 250A of load on your 200A service drop and meter.
You would need to upgrade the 150A panel at the house to a 200A panel, then install the shop panel as a 100A subpanel off the new 200A main.
You would need to upgrade the 150A panel at the house to a 200A panel, then install the shop panel as a 100A subpanel off the new 200A main.
but you got me thinking. There is a 220v line that is already coming out of that box that is disconnected now. I kind of came to the conclusion that it had been used previously for a well pump. It may be only a 30 amp breaker though.
well shoot, its looking better to just run a separate service at the shop and pay the extra $18 a month.
#17
You can install the shop panel as a sub off your current 150A panel, but based on the loads you've described for the shop I really think this will overload your current service. You could do a detailed demand load calculation of the house and shop to determine if the existing 150A service is adequate to support both. Google for "demand load calculation" or get a decent home wiring book from the hardware store to get the details on this calc.
#18
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
well, the "service" to the house is 200Amp and the meter is a 200 amp meter. it is only the breaker panel that feed the house that is 150 amp (the main breaker in the panel is 150 amp).
If I replace just the meter base to get a meter base with double lugs (so I can hook up both panels to the meter base without doubling up on a single set of lugs), I suppose it is theoretically possible to load up 100 amps at the shop and 150 amps at the house but I dont think that is likely. I just dont have anything really huge to load me up that much.
Is there a code requirement that prevents me from having a 150 amp panel for the house and a separate 100 amp panel to the shop bith of which is fed from the 200 amp meter (if there are double lugs on the meter?).
even if I ran my Lincoln stick welder for 30minutes to an hour (which I believe will be my BIGGEST load and only used MAYBE once a year- ive never used it yet btw), that only draws 50 amps. and add to it a couple of lights, i wont be drawing 100 amps at my shop at one time- ever.
the compressor is probably only 15 or 20 amps max and the lift is rated at 17-18 amps and theres no way I'll be lifting and welding at the same time.
I guess I could add up the washer, dryer, hot water heater, stove, over, and dishwasher and AC (or heater to see what they would max me out at)
If I replace just the meter base to get a meter base with double lugs (so I can hook up both panels to the meter base without doubling up on a single set of lugs), I suppose it is theoretically possible to load up 100 amps at the shop and 150 amps at the house but I dont think that is likely. I just dont have anything really huge to load me up that much.
Is there a code requirement that prevents me from having a 150 amp panel for the house and a separate 100 amp panel to the shop bith of which is fed from the 200 amp meter (if there are double lugs on the meter?).
even if I ran my Lincoln stick welder for 30minutes to an hour (which I believe will be my BIGGEST load and only used MAYBE once a year- ive never used it yet btw), that only draws 50 amps. and add to it a couple of lights, i wont be drawing 100 amps at my shop at one time- ever.
the compressor is probably only 15 or 20 amps max and the lift is rated at 17-18 amps and theres no way I'll be lifting and welding at the same time.
I guess I could add up the washer, dryer, hot water heater, stove, over, and dishwasher and AC (or heater to see what they would max me out at)
#19
I suppose it is theoretically possible to load up 100 amps at the shop and 150 amps at the house but I dont think that is likely.
Is there a code requirement that prevents me from having a 150 amp panel for the house and a separate 100 amp panel to the shop bith of which is fed from the 200 amp meter (if there are double lugs on the meter?).
even if I ran my Lincoln stick welder for 30minutes to an hour (which I believe will be my BIGGEST load and only used MAYBE once a year- ive never used it yet btw), that only draws 50 amps. and add to it a couple of lights, i wont be drawing 100 amps at my shop at one time- ever.
#20
Member
Thread Starter
Join Date: Oct 2005
Posts: 122
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The info you have provided is excellent! I thank you again.
I have called the power company and asked them what would I need to do to the service line IF I wanted to (or had to) go up to the next size service (i.e., 320 amp). They said that all I'd need to do is make an appointment with them to come out and shut off the power while I change out the meter base to a 320 amp meter base (and of course, this would be a double lug meter base to set me up for the shop hookup).
I asked them if the line that runs from the pole to my meter box would require upgrading and she said that it wouldnt. She also said I could have one of their engineers come out and do this load calculation to see if I need the larger service for what I need to do.
So it looks like I might have it close to being wrapped up. After I talk with this power guy, I'll let you know what he says and then its GO time! thanks!!
I have called the power company and asked them what would I need to do to the service line IF I wanted to (or had to) go up to the next size service (i.e., 320 amp). They said that all I'd need to do is make an appointment with them to come out and shut off the power while I change out the meter base to a 320 amp meter base (and of course, this would be a double lug meter base to set me up for the shop hookup).
I asked them if the line that runs from the pole to my meter box would require upgrading and she said that it wouldnt. She also said I could have one of their engineers come out and do this load calculation to see if I need the larger service for what I need to do.
So it looks like I might have it close to being wrapped up. After I talk with this power guy, I'll let you know what he says and then its GO time! thanks!!
#21
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I am going to make several assumption and explain some possible options.
Assuming that you presently have a 200 ampere service drop and a 200 ampere meter with 150 ampere service conductors to a 150 ampere main breaker in a 150 ampere panel.
You could install a 200 ampere panel at the meter with a 150 ampere breaker to feed the existing service panel which would then become a sub-panel. A 100 ampere breaker would then be installed in this new (Service) panel to supply the shop.
OR
You MAY (with local utility and AHJ approval) be able to install a 200 ampere fused switch (or single circuit breaker enclosure) next to the meter, with 150 ampere fuses (or circuit breaker, as appropriate), to supply the present service panel, which would then become a sub-panel and install a second 100 ampere fused switch (or single circuit breaker enclosure) to supply the shop. This second option assumes the existing meter has the double taps.
All of these options require the present service panel to become a sub-panel with all of the requirements of isolated neutral and bonded equipment grounding.
Assuming that you presently have a 200 ampere service drop and a 200 ampere meter with 150 ampere service conductors to a 150 ampere main breaker in a 150 ampere panel.
You could install a 200 ampere panel at the meter with a 150 ampere breaker to feed the existing service panel which would then become a sub-panel. A 100 ampere breaker would then be installed in this new (Service) panel to supply the shop.
OR
You MAY (with local utility and AHJ approval) be able to install a 200 ampere fused switch (or single circuit breaker enclosure) next to the meter, with 150 ampere fuses (or circuit breaker, as appropriate), to supply the present service panel, which would then become a sub-panel and install a second 100 ampere fused switch (or single circuit breaker enclosure) to supply the shop. This second option assumes the existing meter has the double taps.
All of these options require the present service panel to become a sub-panel with all of the requirements of isolated neutral and bonded equipment grounding.