apartment wiring loads
Old 11-27-07, 04:43 PM
N
so i'm going to wire my basement for a guest unit... do these calculations make sense while i'm trying to figure out how big a subpanel needs to be?
lighting: 3A (14 23W CFL lighting fixtures)
Heat: 16A (3800W of 240V electric baseboard)
Kitchenette: 45.5A (10A micro, 12.5A toaster, 15A burner, 8A fridge)
misc: 4A (computer, clock, tv)
so i figure if someone's down there with their computer on, listening to the TV, with all the lights on, and is cooking up a storm with all their appliances, they'll be using 70A. so how big should the feeder breaker be going to the basement subpanel?
thanks
Old 11-27-07, 04:52 PM
R
Well, your calculation is off. You cannot add amps at 240 volts to amps at 120 volts. You need to convert them all to the same voltage.
The breaker should be sized for the panel and the wire. You most certainly want a 100 amp panel, so that means you can use any size breaker up to and including 100 amps at the main panel, as long as the wire is sized large enough. I would probably go with a 60 amp breaker.
Old 11-27-07, 05:08 PM
N
So if I convert my 240v heating system to a 120v amp rating I'd add another 16A to my load so I'd have 85A or something. Why would a 60A breaker be sufficient?
Old 11-27-07, 05:50 PM
R
First, nobody runs everything at the same time.
Second, the feeder to the sub panel will be a 240 volt breaker.
Old 11-27-07, 07:21 PM
Received 1 Vote on 1 Post
Third, you want to stay with 240-volt heat.
60 amps is plenty (even if everything is running at the same time).