In my reconfigured kitchen I'm going to have a corner sink. My question is about the placement of receptacles along the countertop.

Do I need to put receptacles behind the sink on each of the walls that define the corner within 24 inches out from the corner? Since there's usable countertop behind the sink it would seem that there might need to be outlets back there to insure that no part of the counter is more than 24" away from an outlet.

However, if the sink defines the start of the usable counter, should I instead install the first receptacle on each of these corner walls at a position adjacent to the edge of the sink, which in this case would be about 36" out from each corner?

Is there some specific wording in the code that deals with this situation?

Thanks,

Dave
 
Sponsored Links
  #2  
Old 12-04-07, 04:37 PM
Member
Join Date: Oct 2007
Location: Delray Beach, FL
Posts: 406
Received 0 Votes on 0 Posts
Yes.
Article 210.52(C)(1).
Draw a line straight back to the wall parallel with the edge of the sink, then measure 24" to the first outlet.
"Receptacles shall not be required on a wall directly behind a range or sink."
 
  #3  
Old 12-04-07, 04:49 PM
Member
Thread Starter
Join Date: Jan 2003
Location: USA
Posts: 77
Received 0 Votes on 0 Posts
Thanks dez. That's exactly what I was looking for.
 
  #4  
Old 12-04-07, 10:04 PM
core's Avatar
Member
Join Date: Jan 2007
Location: Des Moines, IA
Posts: 1,127
Received 0 Votes on 0 Posts
Hmmm may have some bad news. For a corner sink configuration, that exception only applies if the distance behind the sink is less than 18".

You didn't say what that measurement was, but if the far edges of the sink are 36" out from the corner, my _rusty_ trig says that the distance behind the sink is at least 25.5" in your case.

 
  #5  
Old 12-05-07, 12:03 PM
Member
Thread Starter
Join Date: Jan 2003
Location: USA
Posts: 77
Received 0 Votes on 0 Posts
Core,

Thanks for the diagram. That actually helps me alot.

My 36" measurement was taken using a line that was perpendicular to the walls, not parallel to the edges of the sink. Using your diagram, that 36" becomes about 20". I'll just need to get a sink thats deep enough to keep the back within the required 18". On the other hand, it looks like I'll need to add another outlet along one of the walls heading out from the sink. Oh well.

Dave
 
  #6  
Old 12-05-07, 12:14 PM
core's Avatar
Member
Join Date: Jan 2007
Location: Des Moines, IA
Posts: 1,127
Received 0 Votes on 0 Posts
No problem.

Just for the record, that is Exhibit 210.52 from the 2005 NEC. I should have cited credit when I posted that -- guess I accidentally cut the caption off at the bottom.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: