GFCI on a circuit that has 14/2 and 12/2 wiring

I have a circuit in my basement that as 12/2 wiring from the main panel to a number of receptacles. At one receptacle, there's 14/2 wiring going off to a single 60w light switch. At the main panel, the circuit is on a 15A breaker. If I wanted to have the receptacles carry a load of up to 20A, could I change the breaker to a 20A in the main panel and place a 15A GFCI at the receptacle with the 14/2, and have the GFCI moderate the load for the light (ie. 15A GFCI would ensure the 14/2 never carries more than a 15A load)? Or am I stuck with a a maximum 15A for the entire circuit regardless because of the mixed wiring? Thanks.
 
Sponsored Links
  #2  
Old 12-19-07, 06:04 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
No. A GFCI receptacle does nothing to protect against exceeding 15 amps, or 20 amps, or any amount of current. It's only job is to protect against a difference in current between the hot and neutral.

The only way for you to safely change the breaker to 20 amps is to replace that section of 14 gage cable, and any other section of 14 gage cable on the circuit.
 
  #3  
Old 12-19-07, 07:14 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,862
Received 96 Votes on 88 Posts
Or you could split the circuit. Runa new 14/2 cable back to the panel and move all the 14 wire onto a the 15 amp circuit. Then with old circuit only having #12 wire you could install a new 20 amp breaker.
What needs to happen is only #12 wire or larger can be on a 20 amp cicuit. Only #14 wire or larger can be on a 15 amp circuit.
 
  #4  
Old 12-20-07, 12:17 AM
Member
Join Date: Dec 2007
Posts: 6
Received 0 Votes on 0 Posts
Please also keep in mind that the majority of receptacles found in a home are only rated for 15 amp circuits. 15 amp receptacles are not allowed to be installed on a 20 amp circuit. 20 amp receptacles can be identified by the T-slot neutral.
 
  #5  
Old 12-20-07, 05:20 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
In the US it is perfectly legal and common practice to install 15 amp receptacles on 20 amp circuits.
 
  #6  
Old 12-20-07, 06:53 AM
Member
Join Date: Dec 2005
Posts: 257
Received 0 Votes on 0 Posts
Originally Posted by kqresq View Post
Please also keep in mind that the majority of receptacles found in a home are only rated for 15 amp circuits. 15 amp receptacles are not allowed to be installed on a 20 amp circuit. 20 amp receptacles can be identified by the T-slot neutral.
Even I know enough to know this isn't a true statement.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: