GFCI on a circuit that has 14/2 and 12/2 wiring
I have a circuit in my basement that as 12/2 wiring from the main panel to a number of receptacles. At one receptacle, there's 14/2 wiring going off to a single 60w light switch. At the main panel, the circuit is on a 15A breaker. If I wanted to have the receptacles carry a load of up to 20A, could I change the breaker to a 20A in the main panel and place a 15A GFCI at the receptacle with the 14/2, and have the GFCI moderate the load for the light (ie. 15A GFCI would ensure the 14/2 never carries more than a 15A load)? Or am I stuck with a a maximum 15A for the entire circuit regardless because of the mixed wiring? Thanks.
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,970
Received 0 Votes
on
0 Posts
No. A GFCI receptacle does nothing to protect against exceeding 15 amps, or 20 amps, or any amount of current. It's only job is to protect against a difference in current between the hot and neutral.
The only way for you to safely change the breaker to 20 amps is to replace that section of 14 gage cable, and any other section of 14 gage cable on the circuit.
The only way for you to safely change the breaker to 20 amps is to replace that section of 14 gage cable, and any other section of 14 gage cable on the circuit.
#3
Or you could split the circuit. Runa new 14/2 cable back to the panel and move all the 14 wire onto a the 15 amp circuit. Then with old circuit only having #12 wire you could install a new 20 amp breaker.
What needs to happen is only #12 wire or larger can be on a 20 amp cicuit. Only #14 wire or larger can be on a 15 amp circuit.
What needs to happen is only #12 wire or larger can be on a 20 amp cicuit. Only #14 wire or larger can be on a 15 amp circuit.