Multi wire ckts

Is there anything , either code or practical, that would prevent two Tandem breakers with the centers "Handle tied" from being used on a MWBC?
 
Sponsored Links
  #2  
Old 12-20-07, 04:35 PM
Member
Join Date: Mar 2005
Posts: 433
Received 0 Votes on 0 Posts
Well, I suppose as long as they are both mechanically interconnected it would work, and a quick flip of my code book [little outdated] but good none the less doesn't show anything ...
 
  #3  
Old 12-20-07, 05:41 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,117
Received 136 Votes on 122 Posts
IF by two tandem breakers you mean 4 breakers total then not unless both hots land on the same yoke requiring a handle tie. Mulitwire requires one breaker to be on each leg. Most double tandems won't do that.
 
  #4  
Old 12-20-07, 06:29 PM
Member
Join Date: Mar 2005
Posts: 433
Received 0 Votes on 0 Posts
You mean each leg has to be on an opposing phase, correct?
 
  #5  
Old 12-21-07, 12:34 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Originally Posted by Unclediezel View Post
Is there anything , either code or practical, that would prevent two Tandem breakers with the centers "Handle tied" from being used on a MWBC?
no the code is very spefic on this one.

what you refering to the QUAD breaker type like this there is few verison of the quad breaker some have common trip in the center two and outer two is indepent trip and some are common trip on the outer two breaker like what i show ya on the photo.

btw the 08 code cycle is very speficed on this one this will used on MWBC or a single youk [sp] with a split circuit duplex [ only used if two diffrent circuits landed there if the one half of duplex is switched then you dont used the MWBC rules at all ]

Merci, Marc
 
  #6  
Old 12-21-07, 06:20 AM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,117
Received 136 Votes on 122 Posts
Originally Posted by burkej62 View Post
You mean each leg has to be on an opposing phase, correct?
It's a matter terms. Home wiring is only single phase. While commonly refered as two phases it is more properly called legs.
To clarify you must have 240 volts between the two hot wires of a multi wire circuit.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: