I know I've read that in some circumstances you can mark a white wire as hot.
I'm in a situation where I need to create a couple of pigtails and I'm out of 14AWG black wire. I do have quite a number of feet of white wire though, and I'd like to save the trip to the store and added expense if possible.
My questions are:
1) Is this an appropriate circumstance to use a white wire as hot?
2) If so, what is the appropriate amount and style of marking to use? Black electrical tape? A sharpie marker?
Thanks for your help!
Old 01-04-08, 04:17 PM
Unclediezel's Avatar
Switch loops are remarked black when part of a single cable.
Technically remarking anything smaller than #4 is prohibited.
I would use a Sharpie, the full length of the pigtail, If you must.
Old 01-04-08, 04:20 PM
I was looking through another drawer and found a short length of black #12.
I'm assuming it's OK to go ahead and use this as a pigtail on a 15-amp circuit in which the rest of the wires are #14?
Would using the #12 black be preferable to remarking #14 white?
Old 01-04-08, 06:21 PM
pcboss's Avatar
Received 30 Votes on 26 Posts
Yes, an oversized black pigtail would be preferable to the re-identified white.
Old 01-04-08, 06:22 PM
That's what I ended up doing, just using the black #12.