box size

What is the rule of thumb (code) for what size junction box is needed for 10-conductors (12 wire thhn). Also when making the connections are the connected wires counted as one or is it each wire that enters the box counted as one conductor. I plan on connecting THHN to romex to each circut which would then make it 5 thhn hot wires, 5 thhn neutral, 1 thhn ground, and 5-12/2 entering the same box. These connections will all be made in an attic, into a junction box (preferably plastic) with a blank cover.
 
Sponsored Links
  #2  
Old 01-09-08, 11:33 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
each #12 wire need 2.25 cubic inches in the box and what you have there :

5 thhn hot wires= 11.25 cubic inches
5 THHN white wire = 11.25 cubic inches
1 THHN ground wire = 2.25 inches

each 12-2/G NM required 6.75 cubic inches each so you have 5 of them so it will come out 33.75 cubic inches

33.75 + 11.25 + 11.25 + 2.25 = 58.5 cubic inches so you need a box that have at least 60 cubic inches or larger.

if my figures are wrong let me know escpally on ground wire part i am not sure if that nailed right.

but i did not include the romax clamp but they do count as well on metal box.

for that many wire i will like to use 4 11/16 deepwell box or larger [ some call 5X5 box ] or you can use the 6X6X4 box that will easly meet the fill wise.

if other pro feel my figures are wrong let me know [ i am used to figures with metric sized wires and boxes and larger standard wires as well ]

Merci, Marc
 
  #3  
Old 01-10-08, 05:23 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Marc, your figures are wrong, due to the grounds. Forget the fact that it is 12-2, and count each wire properly.

20 current carrying conductors and 1 ground. That makes 21 wires to figure for. That means 47.25 cubic inches forr the wires.
 
  #4  
Old 01-10-08, 11:35 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Thanks Racraft for correcting me on mixed bags.

for some reason i was look like this > after a long day on my work.

i will remember that next time and thank again.

Merci, Marc
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: