Normal Voltage drop on 20 amp circuit?

I have a new home with a 20 amp circuit shared between the kitchen and den. There are 11 recepticles on the circuit. I use the den for my home theater with a surge protector that has a constant line voltage display. With no load (or light load with all equipment on standby), the voltage fluctuates between 118-121. However with a 1500 watt load (toaster oven) in the kitchen, voltage drops from 120 to 113. If I add another 800 watts (toaster) voltage drops to 110. Is this normal, and if not what might the problem be?

Thanks
 
Sponsored Links
  #2  
Old 02-03-08, 02:27 PM
Member
Join Date: Nov 2004
Location: CA
Posts: 2,041
Received 0 Votes on 0 Posts
I am surprised that a kitchen circuit is shared with the den. Your load represents 19 amps. A 9% drop under that load is not outrageous. You will probably experience some "nuisance" breaker trips on this circuit.
 