Rough Inspection Questions
Hi,
I have nearly finished rough wiring an attached addition on my house. I pulled a homeowners electrical permit to do the work as I had done electrical work in the early 90's. Its been awhile so I have some questions about what state things need to be in for rough inspection.
1.) Do I need to remove all romex sheathing in each box prior to the inspection?
2.) Do my grounds need to be tied? If so what is the right way to do the grounds. Do I need to have one ground extension for each device in the box?
3.) How should wires in the external boxes (for outlets and lights) be prepared?
4.) What should be done in the panel for the rough?
Thank You
I have nearly finished rough wiring an attached addition on my house. I pulled a homeowners electrical permit to do the work as I had done electrical work in the early 90's. Its been awhile so I have some questions about what state things need to be in for rough inspection.
1.) Do I need to remove all romex sheathing in each box prior to the inspection?
2.) Do my grounds need to be tied? If so what is the right way to do the grounds. Do I need to have one ground extension for each device in the box?
3.) How should wires in the external boxes (for outlets and lights) be prepared?
4.) What should be done in the panel for the rough?
Thank You
#2
a lot depends on your inspector and what he deems necessary for a rough in inspection
shouldn't be a requirement as it is still exposed after wall closing but it would definately look better and your inspec may want it.
same as #1 and no, you do not need a seperat pigtail for each device. Most resi guys I know loop just one around any devices ground screws and the box ground scew (if metal box). Personally I use individual pigtails for each device. Personal preference. Looks nicer if your joints are all made up at this point but should not be a requirement
Should not have to be made up but I would simply dress them out so all youwould need to do is tie to a lamp feed or device terminal. Looks nicer.
grounding electrode conuctor, neutral bond, main bonding jumper all should be installed. Feeds landed.
If you have branch conductors in the panel, it looks nicer and more inpressive if landed to look nice and neat. That last part should not be neccessary but it allows the inpsepctor more chance to look at your work and help him become comfortable with things. It makes his final easier.
anything you can do so the inspector can see examples of your work will help you and him in the remaining inspections. It allows him to see the quality of your work and allows him to be more comfortable with the overall quality of y our work.
1.) Do I need to remove all romex sheathing in each box prior to the inspection?
2.) Do my grounds need to be tied? If so what is the right way to do the grounds. Do I need to have one ground extension for each device in the box?
3.) How should wires in the external boxes (for outlets and lights) be prepared?
4.) What should be done in the panel for the rough?
If you have branch conductors in the panel, it looks nicer and more inpressive if landed to look nice and neat. That last part should not be neccessary but it allows the inpsepctor more chance to look at your work and help him become comfortable with things. It makes his final easier.
anything you can do so the inspector can see examples of your work will help you and him in the remaining inspections. It allows him to see the quality of your work and allows him to be more comfortable with the overall quality of y our work.
#3
As Nap mentioned, a lot depends on your inspector. My last inspection went exactly as he said... the one prior to that ( I do lots of projects) - I was required to tie the grounds together and run pigtails to each device for the rough in.
#4
Member
Thread Starter
Join Date: Jan 2008
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks Guys
Great response. Ill let you know how my inspection goes.
Two more questions I can think of now.
1st - I have two detectors one smoke and the other heat in the addition. My understanding is that these need to be tied into the existing smoke detector system in the house. Is this correct?
2cnd - My main panel is 200A, sub is 100A, do I need to tie in the sub panel feed to the sub panel for the rough inspection? Obviously the connection will not be made to the main panel, but should the wire be brought into the main panel at this point?
Great response. Ill let you know how my inspection goes.
Two more questions I can think of now.
1st - I have two detectors one smoke and the other heat in the addition. My understanding is that these need to be tied into the existing smoke detector system in the house. Is this correct?
2cnd - My main panel is 200A, sub is 100A, do I need to tie in the sub panel feed to the sub panel for the rough inspection? Obviously the connection will not be made to the main panel, but should the wire be brought into the main panel at this point?
#5
do I need to tie in the sub panel feed to the sub panel for the rough inspection? Obviously the connection will not be made to the main panel, but should the wire be brought into the main panel at this point?
I think it's easier to do most of the work at an earlier stage before other "stuff" gets in the way. It's easier for the inspector to see everything at rough and get his job done fast (which every inspector appreciates).
#6
If possible!!! sometimes there simply is no way to interconnect without tearing out major drywall work.... I've always (6 remodels in 4 years) found that the inspectors are happy with hardwired detectors equipped with battery backup even if they are not interconnected. Not saying it's right - just saying it's so......
#7
Member
Thread Starter
Join Date: Jan 2008
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nap, regarding "grounding electrode conductor, neutral bond, main bonding jumper all should be installed. Feeds landed."
My garage is attached, the subpanel is ~15' from Main panel. I believe a seperate grounding electrode for my subpanel is not required. Is this true?
Thanks
My garage is attached, the subpanel is ~15' from Main panel. I believe a seperate grounding electrode for my subpanel is not required. Is this true?
Thanks
#8
A grounding electrode is not required for a panel in an attached garage. The feeder to the subpanel must be four wires (separate ground and neutral).
#9
Member
Thread Starter
Join Date: Jan 2008
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
4 Wires?
Thanks ipBooks,
My feed wire is 2 gau. aluminum, XHHW. This cable includes a ground and two wires. The ground is tied into the main panel and the sub. Two feed wires from the 100 AMP breaker in my 200 Amp main panel go to the two wires in my 100 Amp main breaker in the subpanel.
What is the fourth wire?
My feed wire is 2 gau. aluminum, XHHW. This cable includes a ground and two wires. The ground is tied into the main panel and the sub. Two feed wires from the 100 AMP breaker in my 200 Amp main panel go to the two wires in my 100 Amp main breaker in the subpanel.
What is the fourth wire?
#10
Subpanels in attached units are required to be fed with a 4 wire feed. Two hots, and insulated neutral and a ground wire. A cable assembly called SER is commonly used.
Do you have a cable like this or is it really 2 hots and a bare? If it is you need to refeed the panel.
Do you have a cable like this or is it really 2 hots and a bare? If it is you need to refeed the panel.