Ground that won't ground

I have been grounding outlets in my apartment that were 3 prong but not grounded. It is an old place with metal boxes and so have been grounding to the screw at the back of the box (with bare 12 gauge wire per code). Things were fine through the livingroom but in the kitchen there are 2 outlets one with a plastic box and one with a metal box. The plastic box is the end of the circuit but the metal is in the middle. The plastic box has a grounding wire hooked up (part of the 3 wire bundle) and "appears" to go to the metal box. It looks like they connected both grounding screws to each other, when I run a grounding wire from the grounding screw on the metal box back to the screw in the box itself (like I did in the livingroom 4 times ) it still does not ground either outlet. Being in an apartment I can't cut holes in the walls and such. I am disabled so on a very limited income (social security) so can't afford an electrician. I owned my own home for 15 years and learned my limited electricle experiance there. Basicly asking....why won't this ground the two outlets like it did in the livingroom? By the way I live in Washington state.
 

Last edited by Davop; 04-07-08 at 02:51 PM. Reason: Give location of problem
Sponsored Links
  #2  
Old 04-07-08, 03:09 PM
HotxxxxxxxOKC's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2006
Location: USA
Posts: 8,044
Received 0 Votes on 0 Posts
If I'm reading this right, you are trying to "ground" a outlet just by having a wire from the receptacle to the outlet box?

A proper ground requires wiring all the way back to the main panel.


Is this your apartment, or do you rent? You cannot legally touch the wiring in a rented apartment.
 
  #3  
Old 04-07-08, 03:22 PM
D
Member
Thread Starter
Join Date: Apr 2008
Location: Washington State
Posts: 4
Received 0 Votes on 0 Posts
Read here in forums

From what I have read in the forums here (if understood correctly) with a metal box you can ground to to the box itself, with a plastic box it must run back to the panel. I do rent but the landlord is not the "type" to help in something like this. I am trying to bring the apartment up to HUD standards to get Section 8 housing allowance do to my disability. The only complaint was that none of the outlets were grounded even though they had 3 prong recepticles. And thank you much for any help you can give
 
  #4  
Old 04-07-08, 03:27 PM
J
Member
Join Date: Oct 2006
Location: Wilmington
Posts: 4,219
Received 0 Votes on 0 Posts
!. 3 prong outlets where there is no ground conductor is not allowed under NEC.
2. As suggested above, there must be a continuous ground conductor that runs all the way back to the main panel. If there is no ground conductor, grounding the outlet to the metal box does nothing.
3. Running a ground conductor to a nearby water or heating pipe is a "bootleg ground" and also not allowed.
 
  #5  
Old 04-07-08, 03:30 PM
D
Member
Thread Starter
Join Date: Apr 2008
Location: Washington State
Posts: 4
Received 0 Votes on 0 Posts
Thank you much

Ok...rats, will reverse what I did even though the testor shows a ground on the boxes I did and go back to the landlord and hope for the best I guess......looks like I will be moving....sigh. Thankl you very much
 
  #6  
Old 04-07-08, 04:00 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
what is happening Davop is there is apparently a metal connection back to the panel that is connected to the metal box. The problem is that unless it is a properly sized grounding conductor as specified by the Nat'l Electrical Code, it is not legal or acceptable. There are rules that must be adhered to for the system to work safely when needed.

Sorry.
 
  #7  
Old 04-07-08, 04:08 PM
D
Member
Thread Starter
Join Date: Apr 2008
Location: Washington State
Posts: 4
Received 0 Votes on 0 Posts
Thanks for words of wisdom

Ah...ok. Maybe why the testor (bought at Wal-Mart) lights all 3 lights instead of the two when wiggled. Indicateing a ground but a bad one, or at least insufficaint. I thank you both for your help and words of wisdom...I shall heed them. The only answer then is to run a ground from the panel to all the outlets in the apartment (really a small old house connected to the complex by one wall) and not something I can do even if I had the knowlege. Once again thank you both.
 
  #8  
Old 04-07-08, 05:15 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
you're welcome
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: