Circuit breaker sizing for garage welder and compressor

Hi,
I have electrical subpanel in my garage and want to install the electrical hardware/wiring for 2 tools. Need help to select correct amperage circuit breakers and wire sizes:

1st tool. Miller MIG welder; 230V 60hz single phase, Input amps at rated output=28, Max Recommended Standard Fuse Rating= 30 (supposed to choose breaker with 'time current curves comparable to a time delay fuse').

2nd tool. Ingersoll Rand air compressor; motor tag reads 230v 60hz single phase, 5 hp, Full Load Amps=22.5

Thanks in advance.
 
Sponsored Links
  #2  
Old 04-14-08, 02:45 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 3 Votes on 3 Posts
Since you have two tools, I would run two circuits, as the welder will probably need a 50 amp breaker. What is he configuration of the plug on the welder? The compressor will be fine on a 30 amp one.
 
  #3  
Old 04-14-08, 02:52 PM
Member
Thread Starter
Join Date: Apr 2008
Posts: 3
Received 0 Votes on 0 Posts
TX for the help!

The welder plug is three prong- one circular prong and two flat prongs parallel with each other but different widths.
 
  #4  
Old 04-14-08, 03:48 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 3 Votes on 3 Posts
  #5  
Old 04-14-08, 04:12 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 10,066
Received 19 Votes on 19 Posts
Hello monster69SCJ,

You say you have a sub panel in your garage but it would be helpful to know what size breaker serves the garage, the wire size and distance.
 
  #6  
Old 04-14-08, 04:49 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,110
Received 136 Votes on 122 Posts
Your manual is stating the welder needs a 30 amp breaker. That means #10 wire.
 
  #7  
Old 04-15-08, 10:49 AM
Member
Thread Starter
Join Date: Apr 2008
Posts: 3
Received 0 Votes on 0 Posts
Yes, the welder plug looks like the photobucket jpg. So welder has a 3-wire cable? How to connect to subpanel since I thought 4-wire would be needed at circuit breaker (red and black wires to breaker poles, white and copper ground to bars)?


I'll check tonight for breaker size serving garage along w/ wire size and length.

Thanks very much to all of you for the help- it's really really been a big help and greatly appreciated!!
 
  #8  
Old 04-15-08, 11:52 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Originally Posted by monster69SCJ View Post
Yes, the welder plug looks like the photobucket jpg. So welder has a 3-wire cable? How to connect to subpanel since I thought 4-wire would be needed at circuit breaker (red and black wires to breaker poles, white and copper ground to bars)?
Only 120/240v appliances such as dryers and stoves usually need four wires. You welder is straight 240v therefore no neutral needed.
 
  #9  
Old 04-16-08, 12:54 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
most resdential stick welder aka buzz box typically have 6-50R allready installed which it mean it is starght 240 volts so you only need two hot conductor and ground wire but however senice you mention your owner manual stated max 30 amp OCPD [ it can be either fuse or circuit breaker ] then you have to follow the manufacter instuction for this

you can run with 10-2w/g NM or #10 THHN/THWN [ if you run this in the conduit ] but however if you go with NM route make sure you remark the white conductor so you know it is hot conductor { use any colour marker as long it is not green}

Now next step the air compressor you should get by with 30 amp breaker but the code have specal area related to the motor you can go larger breaker only if due hard starting then you can go up much as 250% [ per nec code ] but normally 150% is plenty big for most motor useage.

22.5 X 125% = 28.125 so with 30 amp breaker you should be fine there.

and the other thing that if you are in line if sight of breaker box you are ok but if not in sight of breaker box for some reason then you must put in a disconnect switch [ unless your compressor manufacter do have sometype of disconnected switch set up allready ]

Merci,Marc
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: