Outlet vs Breaker Ratings

I actually posted this on the tail of an older question but realized that it might not be looked at so I am reposting as a new question.

In my non-attached shop I have a subbox with a 20A breaker feeding a 20A GFCI followed by downstream 15A non-GFCI outlets. The wiring from the GFCI to the downstream outlets is 14/2 w/ground.
My question is, do the 15A outlets and/or the 14 guage wires have a potential for shorts before the 20A breaker would trip and should they be replaced with 20A outlets and 12 guage wiring? I am making an assumption that I will never have enough load at any one time to exceed 15 amps total.

Thanks for the advice.

Yoandme

P.S. - I am in Washington state
 
Sponsored Links
  #2  
Old 04-15-08, 07:46 PM
HotxxxxxxxOKC's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2006
Location: USA
Posts: 8,044
Received 0 Votes on 0 Posts
That 20 amp breaker needs to go down to a 15amp or replace the 14ga wire with 12. 14ga wire cannot be on a 20amp circuit, but the 15amp receptacles are fine as-is.
 
  #3  
Old 04-15-08, 08:09 PM
Member
Join Date: Nov 2007
Location: (near) Boise, ID
Posts: 442
Received 0 Votes on 0 Posts
The circuit breaker is to protect the wiring, so the breaker must be sized to protect the smallest wire on the circuit.

If there was a short on the 14-2, it could heat up enough to damage the wire before the 20 amp breaker would trip.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: