wall insulation and old wires

In an old house (1935) with a bit of knob and tube remaining, is it safe to blow fiberglass insulation into the walls? Would doing so increase the risk of fire?
 
Sponsored Links
  #2  
Old 04-18-08, 01:56 AM
Member
Join Date: Sep 2004
Location: Saint Louis
Posts: 259
Received 0 Votes on 0 Posts
you need to rewire before insulating.
 
  #3  
Old 04-18-08, 05:22 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Knob and tube wiring cannot be covered with any insulating materials. The K&T needs to be replaced before any insulation can be installed.
 
  #4  
Old 04-18-08, 12:09 PM
JoeTheZombie's Avatar
Member
Join Date: Nov 2005
Location: Idaho
Posts: 216
Received 0 Votes on 0 Posts
Definitely re-wire before insulating. My neighbor's house caught fire because of this exact situation. Only it was attic insulation covering KT, not in-wall.
 