circuit breakers

I am adding a new circuit breaker to a Siemens main panel box. I can find two breakers listed that satisfy my requirements. One is a Q1515. The other is a Q1515NC. The catalog says the "NC" means "no rejection clip". What is a rejection clip on a circuit breaker and which one would I want?
 
Sponsored Links
  #2  
Old 04-21-08, 09:02 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The Q1515NC is a non-CTL (circuit total limiting) breaker. This style would only be used in an older panel. Most fairly modern panels will use the CTL version Q1515.
 
  #3  
Old 04-21-08, 10:16 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Even thru maybe your breaker box may approved to use the tandaem breaker but check with the model number on the breaker box and sometime they will mark the location of the tandem breaker where it can be landed as well.

Most modern breaker box what they approved for tandem breaker they useally located on bottom half of breaker box so just give you a head up in case why some dont fit in one spot so watchout with that one.

Merci,Marc
 
  #4  
Old 04-27-08, 07:41 PM
Member
Thread Starter
Join Date: Apr 2008
Posts: 7
Received 0 Votes on 0 Posts
Ctl

You have given me a new term: (ctl) circuit total limiting. What is it?
 
  #5  
Old 04-27-08, 07:56 PM
Unclediezel's Avatar
Member
Join Date: Dec 2006
Location: Northeastern PA.
Posts: 2,230
Received 0 Votes on 0 Posts
Some breaker panels are certified for use with a given number of breakers. Adding a Tandem or Piggyback would disrupt this certification , because you would change the number of circuits available.

Based on your panel Part #...... It will state how many breaker spaces are physically available, and how many circuits the panel may use.....For example .....30/30 would be 30 spaces/ 30 circuits. On the other hand , a 30/40 would be 30 available spaces, but tandems are permitted , so you would be able to use 40 circuits in 30 spaces.

The rejection clip prevents you from using tandem breakers in
the example 30/30 panel.

CTL----Circuit total limiting.... Would be the limit placed on how many circuits could be used in a given Panel, in relationship to the Number of SPACES
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: