Question Hot Outlet

Yesterday I smelled a strange burning and found out it is an outlet on the middle of a run of outlets. It was hot to touch and nothing was plugged into it. So I shut the circuit off and took the outlet apart. The copper side looks rusty so I'm guessing that's the problem but not sure. I don't use this outlet at all and thought maybe I can just close it off. I did notice that it has three whites wire instead of two. But there are two black wires and one ground (not a green wire type). So what's the best way to deal with this? Close it off or replace the outlet? I don't know how to close it off and like I said it's in the middle. Like to get my bedroom and living room up and running again.
 
Sponsored Links
  #2  
Old 04-23-08, 03:15 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,001
Received 40 Votes on 35 Posts
You should turn the breaker off that controls this receptacle and replace it. You should only place one wire under a screw terminal. Make a loop and place it clockwise around the screw and tighten.

You should have an equal number of blacks and white wires.

What was being used on the same circuit? A high current draw downstream will flow through any upstream receptacles. Any loose connection in the circuit will heat up.
 
  #3  
Old 04-23-08, 04:25 PM
Member
Thread Starter
Join Date: Aug 2006
Posts: 2
Received 0 Votes on 0 Posts
I just noticed there are three blacks also. Two of them are wrapped together so tightly it was hard to see at first. Downstream is in my bathroom and I usually use a blow dryer on the next outlet down from the problem one. Should I not do that? My house is very old and I don't want to put a lot of money into it because the city is buying us out in a year or less. So I'm trying to do the least expensive fixes as possible.
 
  #4  
Old 04-23-08, 05:05 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,001
Received 40 Votes on 35 Posts
Since you have 3 wires and only 2 screws you need to add a short length of wire, called a pigtail, and cap the connection with a twist-on connector commonly called a wire nut. Attach the other end under the screw terminal.

Without rewiring the bathroom circuit there is no way to avoid the current flowing through the receptacles upstream from the bathroom.

I would just replace the receptacle.
 
  #5  
Old 04-23-08, 05:11 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
I will agree with PCboss just pigtail it and run new repectale then you will have peace in your mind with this one.

Merci,Marc
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: