new GFI, 15 amp on 20 amp circuit?


  #1  
Old 05-04-08, 09:20 AM
L
Member
Thread Starter
Join Date: Dec 2003
Posts: 54
Received 0 Votes on 0 Posts
new GFI, 15 amp on 20 amp circuit?

I'm bought a 15 amp GFI outlet for my kitchen that doesn't currently have one. The home was built in the late 70s, and I believe it's the original wiring.

I took the old outlet out, and noticed that the wiring is a heavier gauge than 14. I thought that was odd for a regular outlet, and when I looked at the amp rating on the old outlet, it said 15, so I didn't think much about it.

When I went to shut the breaker off, it's a 20 amp breaker, and I was expecting a 15.

Should I be putting a 20 amp GFI outlet there now, and the original one was not correct? I thought 20 amp outlets have that extra horizontal slot on them, and I've never seen that in a kitchen before.

Can anyone clue me in? Thanks.
 
  #2  
Old 05-04-08, 10:04 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,252
Received 113 Votes on 98 Posts
The 15 amp GFI is fine.

If there is more than 1 physical spot to insert a plug on the circuit 15-amp devices are fine on 20-amp circuits.

The difference between a 15 amp and a 20 amp receptacle is the slot configuration.
 
  #3  
Old 05-04-08, 11:28 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
To add: Kitchen countertop circuits must be 20 ampere. This requirement has been in place for many years.
 
  #4  
Old 05-04-08, 04:32 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,884
Received 325 Votes on 280 Posts
Post your location. If you are in Canada the rules are different.
 
  #5  
Old 05-05-08, 12:46 PM
L
Member
Thread Starter
Join Date: Dec 2003
Posts: 54
Received 0 Votes on 0 Posts
Cool, thanks for the info. I'm in the us, Phoenix area.
 
 