Suibpanel grounding

Hi again.

In my remodel, I am having to modify both my subpanels so that they have a separate grounds and neutrals.

In my smaller 100A subpanel, the ground wire is a tad short to reach where my ground bus bar will be.

Is it OK to use a lug to attach the ground wire to the metal panel box and have the ground bar a short distance away, obviously also attached to the metal box?

Thanks.
 
Sponsored Links
  #2  
Old 05-05-08, 09:33 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Ground wire for a 100A panel should be #8 copper, so you can just use a big wirenut to extend it. You could also use something like a crimp-on buttsplice connector to length the wire. You could also install an add-on ground bar where the wire will reach.
 