New Construction Wiring Questions

To run the appliances what do i need? do i need 3 wire or can i use 2 wire for some?

What size and type of wire for Dryer, Stove, Microwave, and Air conditioner. I have heard sometimes you need a neutral and sometimes you dont. When and why is this the case? This is new residential construction
 
Sponsored Links
  #2  
Old 05-18-08, 03:56 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Every one of those things has a different answer, and each answer would be a long answer, and we'd have to ask you a hundred questions about the appliances before we knew what to say.

You need a book. In fact, you need several books. Visit your home center and browse their selection. If you are really going to do significant wiring in a new house, you probably need one of those books that cost about $75. It would not be practical for us to try to type out the contents of such a book in this forum.

If you see specific things in the book that you would like us to help clarify, please come back and ask.
 
  #3  
Old 05-18-08, 04:01 PM
Member
Thread Starter
Join Date: May 2008
Posts: 5
Received 0 Votes on 0 Posts
Appliance questions

it is really not that complicated if you are wiring for a house to be sold you do not know what type of applicances the owners will choose
 
  #4  
Old 05-18-08, 04:15 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
If you are doing this for a house to be occupied by somebody else, then almost all states would require you to be a licensed electrician.

In general, an electric clothes dryer would require 10/3, a gas clothes dryer would need 12/2, a stove 6/3, a microwave 12/2, and an whole-house air conditioner 6/3. Sometimes the stove and A/C would require less, but 6/3 would give more options.

You need a neutral for all 120-volt appliances, and for 240-volt appliances that have 120-volt accessories or components (such as all clothes dryers and many stoves).
 
  #5  
Old 05-18-08, 04:46 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
For the central A/C unit the outdoor unit useally use #10-2 most of the time [ the circuit breaker size will varies depending on the unit itself ] but the indoor unit sometime called air handling unit and if this air handling unit do NOT have electric heating elements in there then pretty much SOP is use 12-2 with 20 amp breaker unless you got electric heat that will pretty much determend on the size of the heater itself.

For the ranges most common used either 8-3 or 6-3 W/G but most of my time i useally use the latter one due some of the range have much as 12 KW rating so that make sense and make sure you use 4 wire receptale there as well if you run new wires in there. [ 8/3 is good with 40 amp breaker while 6/3 is good with 50 amp breaker { copper wires}]


For the dryers it pretty common to use 10-3W/G romex cable with 30 amp breaker. then again if this is a new wire you have to run 4 wire receptale also.

For the SABC [ small appalince branch circuit ] per NEC code it will reqired min of 2 circuits but however it pretty common to run more than 2 anyway.

Check with your codes it may change a little realted to the circuit layout.

If you are going to sell the house pretty quick i will really advise ya get ahold of electrician to do this.

Merci,Marc
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: