240 volt beaker problem
#1
Member
Thread Starter
Join Date: May 2008
Posts: 3
Received 0 Votes
on
0 Posts
240 volt beaker problem
Hello hopefully somebody can help me ... I am trying to install a 240 volt receptacle in my garage. heres my problem when i install the dual pole breaker into the panel i only get 120 on each pole but when i test both poles i get a reading of 0 , i thought it maybe was my breaker but i tried it on two different ones .. any ides??? using federal stab-lok breakers
#2
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes
on
0 Posts
You installed a tandem (AKA twin or skinny) breaker. Except is a very few panels (e.g., certain GE panels), you cannot get 240 volts from that. Generally, you need a double-wide breaker to get 240 volts, although you can sometimes save space by using one quad breaker to get two 240-volt circuits.
#3
Member
Join Date: Jan 2004
Location: Oregon
Posts: 1,219
Received 0 Votes
on
0 Posts
Inside a normal residential breaker panel, there are two 'busses' which connect the main supply to the breakers. In a normal installation, each bus is 120V to neutral, and 240V to the other bus.
The most likely situation is that you purchased a 'skinny' or 'tandem' breaker. This is actually a pair of single pole breakers that fits into a single slot. Both of these breakers connect to the same bus, so that you will never get 240V. Additionally, the two poles don't have a proper 'common trip' needed for a 240V application.
Sometimes (very rarely) the two busses are connected to the same leg of the supply, making a '120V' panel. Such a panel cannot supply 240V loads, even with proper breakers.
Certain breaker panels actually have true double pole skinny breakers; depending upon the position in the panel the two poles will end up on the same or different busses; to get 240V you need the two poles on different busses.
Finally, if one of the supply legs has been damaged and disconnected from the POCO supply, you can still see voltage on that buss as current passes through various 240V loads from the working leg. You would be seeing significant electrical problems throughout your house if this were the case.
-Jon
The most likely situation is that you purchased a 'skinny' or 'tandem' breaker. This is actually a pair of single pole breakers that fits into a single slot. Both of these breakers connect to the same bus, so that you will never get 240V. Additionally, the two poles don't have a proper 'common trip' needed for a 240V application.
Sometimes (very rarely) the two busses are connected to the same leg of the supply, making a '120V' panel. Such a panel cannot supply 240V loads, even with proper breakers.
Certain breaker panels actually have true double pole skinny breakers; depending upon the position in the panel the two poles will end up on the same or different busses; to get 240V you need the two poles on different busses.
Finally, if one of the supply legs has been damaged and disconnected from the POCO supply, you can still see voltage on that buss as current passes through various 240V loads from the working leg. You would be seeing significant electrical problems throughout your house if this were the case.
-Jon
#7
Federal Pacific "STABLOKS" are a known problem, and strong consideration to replacing the panel is advised.....
Not necessarily side to side....But it is entirely possible to put a Stablok Breaker in the wrong slot, and cause exactly what you had. Moving it over 1 full space will cure the symptoms.
Not necessarily side to side....But it is entirely possible to put a Stablok Breaker in the wrong slot, and cause exactly what you had. Moving it over 1 full space will cure the symptoms.