Wire size?

Installing a steam generator. 240v, single phase. 38 amps. Documentation says a 60amp breaker. What size wire should I use? #10 or #8? Also, the generator is going to be 3 feet from the main panel. Should I put the wiring in coduit or just use clamps? See any need for a disconnect between the unit and the panel?

Thanks!
 
Sponsored Links
  #2  
Old 05-22-08, 07:29 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
does it list a minumum circuit ampacity?

If not, then you would need to use #6. #8 is not good for 60 amps.

and to the install method: personal choice.

No need for a disconnect due to the fact of the proximity to the panel.
 
  #3  
Old 05-23-08, 08:36 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
With a 60A breaker, #6 copper hots with #10 ground would be the correct size. THHN conductors in conduit or 6/2g NM-B Romex cable would be okay.

I'm surprised the manuf. didn't suggest 50A breaker: 38A * 125% = 47.5A. If that was the case, #8 copper hots with #10 ground in conduit would be okay (not 8/2g NM-B Romex).
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: