15 amp breaker trips without breaking
#1
Member
Thread Starter
Join Date: Jun 2008
Posts: 9
Received 0 Votes
on
0 Posts

Hi,
We seem to have a electrical issue in our kitchen. Our fridge is on a 15 amp circuit with 5 counter recepticles and also 2 recepticles in the basement (one which feeds a sump pump) and 2 outside GFI recepticles which are generally not in use. Is this too much?
I've already replaced the 15amp breaker with a new one.
Once in a while the circuit still will blow but the breaker does not trip. What does this indicate? Would it be a problem to boost it to 20amp or should I get an electrician to split the load up on this circuit? Thanks for any help on this.
We seem to have a electrical issue in our kitchen. Our fridge is on a 15 amp circuit with 5 counter recepticles and also 2 recepticles in the basement (one which feeds a sump pump) and 2 outside GFI recepticles which are generally not in use. Is this too much?
I've already replaced the 15amp breaker with a new one.
Once in a while the circuit still will blow but the breaker does not trip. What does this indicate? Would it be a problem to boost it to 20amp or should I get an electrician to split the load up on this circuit? Thanks for any help on this.

#2
This must be rather old as it does not meet any code in existence for more than thirty years.
You MAY NOT increase the size of the circuit breaker unless all of the wiring in this circuit is a minimum of #12 copper. Since it already has a 15 ampere breaker it MUST be assumed to be smaller than #12 until proven (by inspection) to be #12 or larger.
You can split the load to one or more new circuits but you will have to follow current code when doing so. This can be a DIY job.
You MAY NOT increase the size of the circuit breaker unless all of the wiring in this circuit is a minimum of #12 copper. Since it already has a 15 ampere breaker it MUST be assumed to be smaller than #12 until proven (by inspection) to be #12 or larger.
You can split the load to one or more new circuits but you will have to follow current code when doing so. This can be a DIY job.
#3
Breakers trip due to too much current flowing through them. GFI's trip due to an imbalance of current.
#4
If the breaker is not tripped how do you get the power back? Sounds like you might have a loose connection somewhere.
#5
Member
Thread Starter
Join Date: Jun 2008
Posts: 9
Received 0 Votes
on
0 Posts
I have isolated which circuit it is........
I have isolated which circuit it is. I know it's not tripped because it's not orange, however when I reset it the power comes back on. I've heard pops or clicks sometimes at the main board. Like I said earlier, I've changed it out to a new one and made sure the snaps are tight. Power still goes out every once in a while.
#6
Member
Thread Starter
Join Date: Jun 2008
Posts: 9
Received 0 Votes
on
0 Posts
The GFI's are on the same circuit and no they don't trip. Nothing trips. The circuit breaker looks normal in the main box. Simply we are in the kitchen, and the power goes and off goes the fridge. I run down to the circuit box and reset the untripped breaker ( I know which one it is) and the power comes back on.
#7
Member
Thread Starter
Join Date: Jun 2008
Posts: 9
Received 0 Votes
on
0 Posts
The house is 45 years old............
This must be rather old as it does not meet any code in existence for more than thirty years.
You MAY NOT increase the size of the circuit breaker unless all of the wiring in this circuit is a minimum of #12 copper. Since it already has a 15 ampere breaker it MUST be assumed to be smaller than #12 until proven (by inspection) to be #12 or larger.
You can split the load to one or more new circuits but you will have to follow current code when doing so. This can be a DIY job.
You MAY NOT increase the size of the circuit breaker unless all of the wiring in this circuit is a minimum of #12 copper. Since it already has a 15 ampere breaker it MUST be assumed to be smaller than #12 until proven (by inspection) to be #12 or larger.
You can split the load to one or more new circuits but you will have to follow current code when doing so. This can be a DIY job.
#8
Member
Join Date: Nov 2005
Location: USA
Posts: 296
Received 0 Votes
on
0 Posts
nova_gh
master electrician
#9
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes
on
0 Posts
It indentcated that the circuit breaker tripped due from either overload or short circuit.
Do not reset the breaker until you know what causing the breaker to trip in first place if overload all you have to is unplugged hevey power useage device.
But with short circuit this is more serious matter you have to deal with it.
Now you mention alum wire in your house.
I just want to make sure you understand there is two diffrent type of alum wires you see there.
If the wire look like plastic coating and the wire itself is all silver no copper colour at all then you got the legit alum wire there.
But however.,, if the wire look like cloth with rubber coating then you got copper tinned wire then you got legit copper wire.
Anyway with alum wire it will be little more tricky to do the safe proper connecton or termating them.
There is not many products in the market is approved to termated or connecton with alum wires.
{ IF you used the purple wire nuts please let me know there is a safe way to do this }
If you have leigt tinned copper wire then you can termated in standard way as modern copper wires is now.
Merci,Marc
#10
I have isolated which circuit it is. I know it's not tripped because it's not orange, however when I reset it the power comes back on. I've heard pops or clicks sometimes at the main board. Like I said earlier, I've changed it out to a new one and made sure the snaps are tight. Power still goes out every once in a while.
What type of items are you using on the circuit? How many watts?
#11
By the fact that you turning the breaker off then on indicates that it is in fact tripping. There are too many things on this circuit and is causing the breaker to trip.
Not only is this a nuisance, but also considering that it's aluminum wiring, you should probably have a licensed electrician come out and inspect this circuit in particular. Aluminum wiring is known to loosen up over time, especially with often used circuits. As stated previously, current code would not allow a circuit to be used throughout the kitchen and house this way because of the draw of the fridge and other kitchen appliances.
#12
Member
Thread Starter
Join Date: Jun 2008
Posts: 9
Received 0 Votes
on
0 Posts
thanks for feedback
Some breakers have a window that turns red/orange when the breaker trips, others, click off to a middle position. Some breakers are easy to see when they are tripped, others look like they are still on.
By the fact that you turning the breaker off then on indicates that it is in fact tripping. There are too many things on this circuit and is causing the breaker to trip.
Not only is this a nuisance, but also considering that it's aluminum wiring, you should probably have a licensed electrician come out and inspect this circuit in particular. Aluminum wiring is known to loosen up over time, especially with often used circuits. As stated previously, current code would not allow a circuit to be used throughout the kitchen and house this way because of the draw of the fridge and other kitchen appliances.
By the fact that you turning the breaker off then on indicates that it is in fact tripping. There are too many things on this circuit and is causing the breaker to trip.
Not only is this a nuisance, but also considering that it's aluminum wiring, you should probably have a licensed electrician come out and inspect this circuit in particular. Aluminum wiring is known to loosen up over time, especially with often used circuits. As stated previously, current code would not allow a circuit to be used throughout the kitchen and house this way because of the draw of the fridge and other kitchen appliances.