low voltage

I Have an elecrical outlet that only shows 80 volts. The plug has 2 brown wires on one side and 2 white on the other side. I checked it 3 times and checked other plugs that read 110.
Any Ideas?
 
Sponsored Links
  #2  
Old 06-30-08, 02:11 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Plug a lamp into that receptacle, switch it on and test the voltage again. I bet that you will find the bulb does not light and the actual voltage is zero. Search for "phantom voltage" for an explanation.

Your likely problem is a loose or broken wire at this receptacle or at a device upstream in the circuit. The remedy is to open up all of the receptacles, switches and light fixtures on this circuit until you find the weak connection. Move any backstabbed wires to the adjacent screw terminals. The problem is usually at the first non-working receptacle or last working receptacle.
 
  #3  
Old 06-30-08, 02:59 PM
Member
Join Date: Jun 2008
Location: Maryland
Posts: 298
Received 0 Votes on 0 Posts
120v is the maximum into a high-impedance meter for phantom voltages due to Romex interconductor capacitance, 60v if one of the Romex leads is grounded, something in the middle if you're using a 1000 ohms/volt analog meter.

This line might also be in series with some load, somewhere. See if this voltage stays when using a hair dryer. Pulling 10A should drop you about 3v.
A bad neutral connection can give you above and below 120v depending on what else in the house is switched on.
 
  #4  
Old 06-30-08, 09:24 PM
Member
Join Date: Dec 2006
Location: orange county
Posts: 285
Received 0 Votes on 0 Posts
Digital voltmeters are very misleading when used for checking voltages for house-wiring. Electricians use what's called a "wiggy". HD sells them for about 14 bucks.
 

Last edited by sidecutter; 06-30-08 at 09:26 PM. Reason: typing error
  #5  
Old 06-30-08, 09:37 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
Inflation hits everywhere, they're about $20.

http://www.homedepot.com/webapp/wcs/...ctId=100341461
 
  #6  
Old 07-01-08, 07:21 AM
Member
Join Date: Jun 2008
Location: Maryland
Posts: 298
Received 0 Votes on 0 Posts
"wiggy".

The specs on the Wigglesworth says "up to" 5 mA input current, so it may trip an upstream GFI.

I kinda' prefer my 4-1/2 digit DVM along with several load resistors.

A 100 ohm 100w rheostat comes in handy when you don't know if you're looking into a short circuit or 600w worth of incandescent lamps, but a 100 w bulb works almost as well. Most meters have trouble resolving milliohms.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: