Any voltage drop in 475ft of 2-2-4 aluminum wire
My cabin is 475 ft from the power meter on my land and I need to run a line to it. Im going to use 2-2-4 aluminum wire and would have an electric stove ,water heater, well pump and a few kitchen appliances as a load, do you think that the 2-2-4 wire will work ok without too much voltage drop?
#2
Even with a modest predicted load of 50A, you still have nearly 6% voltage drop which is too high in my opinion. Code recommends you limit voltage drop to 2% on feeders; however that is not always practical. I think you should at least strive for 5% which would require #2/0 aluminum minimum.
I should also note that voltage drop is not a required design parameter based on the code, so you can use the #2 aluminum for a 100A service at 475', it's just not a good idea to do so. Code only covers safety, not good design practices.
#3
Unforetally with that much distance if you have electric stove , electric water heater on you will really face serious voltage drop.
You will need much larger cable size to handle that kind of load typically like 2/0 may squeak by. but better use 3/0 alum wire or larger if you can get ahold of it in the big box store otherwise electrical supply centre will have much larger one on hand.
Merci,Marc
You will need much larger cable size to handle that kind of load typically like 2/0 may squeak by. but better use 3/0 alum wire or larger if you can get ahold of it in the big box store otherwise electrical supply centre will have much larger one on hand.
Merci,Marc