i need a 220v extension for an window AC
about 28,000btu. can i get a 50 foot #10-2/g in a stranded copper and not deal with the romex solid copper? i will install the two connectors for the ends to match my plugs.
thanks in advance......
thanks in advance......
#2
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#4
Member
Join Date: May 2005
Location: South Florida
Posts: 121
Upvotes: 0
Received 0 Upvotes
on
0 Posts
the stock at home depot/lowes varies by location, they should have it but I would call first. If not a local electric supply would be your best bet.
Also remember that SJ cord and Romex wire numbers are not the same. Meaning
10- 3 SJ = Black, White, Ground
10- 3 Romex = Black ,white, red, ground
So if you need a Red, ask for 10-4 SJO cord
Also remember that SJ cord and Romex wire numbers are not the same. Meaning
10- 3 SJ = Black, White, Ground
10- 3 Romex = Black ,white, red, ground
So if you need a Red, ask for 10-4 SJO cord
#7
Extension cords are intended for temporary use only. You will need to install a permanent receptacle. What are the specs for the receptacle (amps/number of wires) you are plugging into? It was intended for an AC wasn't it?
#8
You definitely don't want to run a 50' extension cord for an air conditioner. Hard wire it correctly to the location. It is the only way to do it safely.
#9
Member
Join Date: Jul 2008
Location: Kingston, PA
Posts: 131
Upvotes: 0
Received 0 Upvotes
on
0 Posts
...against the recommendations of those who are concerned about code violations and safety...
please see the latest comments on your other post
willis
please see the latest comments on your other post
willis
#10
I merged your threads into one because they cover the same problem.
A 28kBTU air conditioner is a pretty big unit, especially to run at a distance of 50'. Without knowing the nameplate specs of the unit, I'm not sure the #10 SJO is sufficient for this A/C.
Furthermore, 50' is a long cord to use safely. Make sure it is not covered by any carpets or rugs, and that it does not present a tripping hazard such as crossing a doorway or hallway.
A 28kBTU air conditioner is a pretty big unit, especially to run at a distance of 50'. Without knowing the nameplate specs of the unit, I'm not sure the #10 SJO is sufficient for this A/C.
Furthermore, 50' is a long cord to use safely. Make sure it is not covered by any carpets or rugs, and that it does not present a tripping hazard such as crossing a doorway or hallway.
#11
A 28K btu A/C @ 240 volts will draw anywhere from 24 to 28 amp very easy and with 50 foot extenison cord that part I am not too crazy but it can be done but my main conderastion is the amout of current going thru the 10-3 SJO cord.
Is there any reason why can't you run a new romex cable for the A/C unit ??
Merci,Marc
Is there any reason why can't you run a new romex cable for the A/C unit ??
Merci,Marc