wiring for outdoor spa
#1
Member
Thread Starter
Join Date: Jul 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
wiring for outdoor spa
I'm installing a hot tub. It's requires 240v, 40/50amps, and is 50' away from the main panel where I will connect to. I need some advice...If I wire the spa control panel directly to a 50 amp gfci breaker with #8 wire, will it meet nec code?
Thanks,
Dave
Thanks,
Dave
#2
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Whats the actual load of the unit? and what wiring method were you going to use?
#3
Is it 40 or 50?
Essentially, but there's an awful lot of details to make it compliant. The type of #8 is important; for example, NM-B or UF-B cable is not allowed. THWN in conduit is allowed.
You'll also need a disconnect at least 5' from the tub, but within line-of sight.
If I wire the spa control panel directly to a 50 amp gfci breaker with #8 wire, will it meet nec code?
You'll also need a disconnect at least 5' from the tub, but within line-of sight.
#4
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It is allowed inside of a dwelling unit though... Pools, spa's, and the like IMO are not DIY jobs, there are just way to many codes.
#5
Member
Join Date: Jul 2008
Location: USA
Posts: 339
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This is a good place to start for more info....
http://www.pacificspasales.com/page3...74/page74.html
Home depot sells a disconnect GFCI box. It would go a min. of 5' from the tub and then be wired to the house via conduit and wiring as specified. In this case you would use a standard double pole breaker in the inside panel with the proper rating.
You need to pay particular attention to grounding and bonding. It is absolutely important it be done right.
http://www.pacificspasales.com/page3...74/page74.html
Home depot sells a disconnect GFCI box. It would go a min. of 5' from the tub and then be wired to the house via conduit and wiring as specified. In this case you would use a standard double pole breaker in the inside panel with the proper rating.
You need to pay particular attention to grounding and bonding. It is absolutely important it be done right.
#6
Member
Join Date: May 2001
Location: Dry Side of Washington State
Posts: 685
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#7
Member
Thread Starter
Join Date: Jul 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the replies,
I'll take your advice dsc3507 and get the disconnect and do it the safest way.
50 amp gfci disconnect, #6 wire in rigid conduit, 60 amp breaker at the main. I'll go visit the local inspector tomorrow.
Thanks guys
I'll take your advice dsc3507 and get the disconnect and do it the safest way.
50 amp gfci disconnect, #6 wire in rigid conduit, 60 amp breaker at the main. I'll go visit the local inspector tomorrow.