wiring for outdoor spa


  #1  
Old 07-24-08, 11:44 AM
D
Member
Thread Starter
Join Date: Jul 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
wiring for outdoor spa

I'm installing a hot tub. It's requires 240v, 40/50amps, and is 50' away from the main panel where I will connect to. I need some advice...If I wire the spa control panel directly to a 50 amp gfci breaker with #8 wire, will it meet nec code?

Thanks,
Dave
 
  #2  
Old 07-24-08, 12:59 PM
C
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by dmctexas
I'm installing a hot tub. It's requires 240v, 40/50amps, and is 50' away from the main panel where I will connect to. I need some advice...If I wire the spa control panel directly to a 50 amp gfci breaker with #8 wire, will it meet nec code?

Thanks,
Dave

Whats the actual load of the unit? and what wiring method were you going to use?
 
  #3  
Old 07-24-08, 01:03 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Originally Posted by dmctexas
It's requires 240v, 40/50amps
Is it 40 or 50?

If I wire the spa control panel directly to a 50 amp gfci breaker with #8 wire, will it meet nec code?
Essentially, but there's an awful lot of details to make it compliant. The type of #8 is important; for example, NM-B or UF-B cable is not allowed. THWN in conduit is allowed.

You'll also need a disconnect at least 5' from the tub, but within line-of sight.
 
  #4  
Old 07-24-08, 01:12 PM
C
Member
Join Date: Aug 2007
Posts: 114
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by ibpooks
The type of #8 is important; for example, NM-B or UF-B cable is not allowed.
It is allowed inside of a dwelling unit though... Pools, spa's, and the like IMO are not DIY jobs, there are just way to many codes.
 
  #5  
Old 07-24-08, 01:17 PM
D
Member
Join Date: Jul 2008
Location: USA
Posts: 339
Upvotes: 0
Received 0 Upvotes on 0 Posts
This is a good place to start for more info....

http://www.pacificspasales.com/page3...74/page74.html

Home depot sells a disconnect GFCI box. It would go a min. of 5' from the tub and then be wired to the house via conduit and wiring as specified. In this case you would use a standard double pole breaker in the inside panel with the proper rating.

You need to pay particular attention to grounding and bonding. It is absolutely important it be done right.
 
  #6  
Old 07-24-08, 01:59 PM
T
Member
Join Date: May 2001
Location: Dry Side of Washington State
Posts: 685
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #7  
Old 07-24-08, 06:06 PM
D
Member
Thread Starter
Join Date: Jul 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies,
I'll take your advice dsc3507 and get the disconnect and do it the safest way.
50 amp gfci disconnect, #6 wire in rigid conduit, 60 amp breaker at the main. I'll go visit the local inspector tomorrow.

Thanks guys
 
 