Hello and thanks for your suggestions and advice. I would like to set a 30 amp receptical outside for the generator to plug into. Have this line backfeed into the panel box (with the main breaker off), flip all other breakers off and only have 1 or 2 circuits open for lights, fans, small tv, etc. Nothing heavy like the well, ac., etc. I have a security light on the utility pole outside which would notify me of power back on. I'll just have to wait till dark to find out ! Thanks again for the advice. Let's have a great day and God Bless America.......
#2
You need a dedicated safety device to prevent backfeed in the event the main breaker is flipped on while on generator power. This can be a simple isolation switch or a more complex siwtch box. Here are examples:
http://www.electricgeneratorsdirect....r-switches.php
Here's some additional reading material:
http://www.smps.us/transferswitch.html
http://www.electricgeneratorsdirect....r-switches.php
Here's some additional reading material:
http://www.smps.us/transferswitch.html
#3
Another common backfeed prevention device is an interlock kit, which is a set of levers and sliders which mount to the panel and only allow the main or the generator to be active, but not both. Most of the major manufacturers produce them for their panels, and there are also aftermarket kits such as Interlock Kit.
The outside receptacle to plug in the generator should actually be an inlet (instead of an outlet), so you don't have to use a male-male suicide cord. The interlock site also has some examples of inlet boxes, although their prices are too high on that item.
The outside receptacle to plug in the generator should actually be an inlet (instead of an outlet), so you don't have to use a male-male suicide cord. The interlock site also has some examples of inlet boxes, although their prices are too high on that item.