Is it a blown circuit?

Reply

  #1  
Old 10-15-08, 11:25 AM
Member
Thread Starter
Join Date: Oct 2008
Location: Northwest
Posts: 1
Received 0 Votes on 0 Posts
Is it a blown circuit?

Last night we had two heaters plugged into our room and the TV on and then all the sudden everything went off so we must have blown a circuit, but when we went to the breaker box all them were in the correct positions and none appeared to have been tripped. We clicked all over and back just to make sure, but still no power in our master bedroom area. Any thoughts?
 
Sponsored Links
  #2  
Old 10-15-08, 12:20 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Even one electric heater should not have been on a shared circuit. Two on the same circuit is way too much. A couple of possibilities come to mind.

First are there still any receptacles on the affected circuit that still work? If so that rules out a bad breaker.

Second and more likely possibility is a failed connection. That heavy a load could easily do it. You will need to open up every receptacle and light on the circuit and check the connections. I'd start with the two places you had the heaters plugged in. Any back stabbed connections on receptacles need to be moved to the screws. Any wire nut connections need to be redone and wire nuts replaced. Any screw connections checked for tightness.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: