having a hot tub installed...only two lines (black & red) have been strung to back of garage...waiting for sub-panel and tub. my tub people tell me that I need a three-wire feeder (hot-hot-neutral) and my electrical man says that the 'tub' will be grounded by wire to the pipe that ran the wire...what little i do know (nothing) tells me that a 4' rebarb could be drove into the ground next to the tub for my ground...and exactly why is a 'neutral' used for? Distance from main breaker to sub-panel is 75'
Distance from sub-panel to 'tub' will be right under 10'
Distance from sub-panel to 'tub' will be right under 10'
#2
A neutral carries the unbalanced current from tub control circuits and lighting that are 120 volts.
You will NOT drive a rebar or grounding rod at the tub.
You will also need a 120 volt GFI protected receptacle with a weatherproof in use cover. IIRC no closer that 10 foot.
There may be bonding issues depending on your specific circumstances.
You will NOT drive a rebar or grounding rod at the tub.
You will also need a 120 volt GFI protected receptacle with a weatherproof in use cover. IIRC no closer that 10 foot.
There may be bonding issues depending on your specific circumstances.
#3
Your local code may have an exception which allows the proposed installation.