Portable Generator Hookup?
#1
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Portable Generator Hookup?
I have read alot about installing elect. transfer switches and in my situation, I have an exsting exterior disconnect was required to be installed when I built. Could I pull that disconnect when I have power failure AND turn off my interior power panel main ? Would that safely isolate my home from backfeeding into the power grid? And IF I do have to install a transfer switch could I tap into the the power between the disconnect switch and the interior panel to install the transfer switch ? Would that be the easier route than tearing into my interior wall/power panel to install it there? I need some advice, thanks,
Kenny
Kenny
#2
I have read alot about installing elect. transfer switches and in my situation, I have an exsting exterior disconnect was required to be installed when I built. Could I pull that disconnect when I have power failure AND turn off my interior power panel main ? Would that safely isolate my home from backfeeding into the power grid?
Kind of hard to say with out seeing it, but I see no issues with that plan.
Last edited by Tolyn Ironhand; 11-18-08 at 09:03 AM.
#3
Member
Join Date: Aug 2008
Location: Guam
Posts: 37
Upvotes: 0
Received 0 Upvotes
on
0 Posts


#4
Article 720 requires simultaneous disconnection of the main when the emergency power is turned on.
Separate pieces of equipment as you have described does not meet the requirements of the NEC.
You need to install a manual double throw switch or interlock kit depending on the configuration of your service.
Separate pieces of equipment as you have described does not meet the requirements of the NEC.
You need to install a manual double throw switch or interlock kit depending on the configuration of your service.