Maximum outlet per a curcuit


  #1  
Old 11-21-08, 01:51 PM
D
Member
Thread Starter
Join Date: Nov 2008
Location: Spokane wa
Posts: 2
Received 0 Votes on 0 Posts
Maximum outlet per a curcuit

What is the maximum number of outlets I can put on a 15A curcuit? 20A ?
How far apart should outlet be? I heard every 6 feet?
That is alot of outlets.The area is going to be used as a second living area.

I finsihing my basement in Spokane Wa. I have a room that is 48X15.

Thank you
David
 
  #2  
Old 11-21-08, 02:18 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 45 Votes on 43 Posts
Originally Posted by dcrcjcdc View Post
What is the maximum number of outlets I can put on a 15A curcuit? 20A ?
The code does not specify a number, however a good rule of thumb for general-purpose receptacles is 8 for a 15A circuit and 12 for a 20A circuit.

How far apart should outlet be? I heard every 6 feet?
The rule is that no point along the base of the wall can be more than 6' from a receptacle. That generally means you need to have one within 6' of each doorway and then every 12' after that. You measure along the base of the wall and can continue around corners; you cannot measure across doorways, fireplaces, and other such breaks in the wall. Every wall segment 24" or greater needs at least one receptacle.

The area is going to be used as a second living area.
If your area is on 2008 NEC, you will need an AFCI breaker for any circuits supplying this room.

I finsihing my basement in Spokane Wa. I have a room that is 48X15.
That's a pretty big room. I'd probably do one 15A circuit for lighting and two 20A circuits for receptacles, possibly three if you have a specific area that will be used for office equipment or home theater.
 
 