Just want to confirm... (subpanel)

Reply

  #1  
Old 12-01-08, 04:51 PM
TomZ1's Avatar
Member
Thread Starter
Join Date: Sep 2003
Location: New Hampshire
Posts: 174
Received 0 Votes on 0 Posts
Just want to confirm... (subpanel)

...my understanding.

Subpanel in a separate building (shed). If it has more than 6 circuits it needs to have a disconnecting means.

I take this to mean a sub with more than 6 circuits (throws) would actually have to be a main breaker panel rather than a main lug panel.

Correct?

 
Sponsored Links
  #2  
Old 12-01-08, 06:23 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,128
Received 92 Votes on 82 Posts
Correct.

You can back feed a breaker rather then use the main lugs. Or you can buy a separate disconnect and run from the disconnect to the panel.
Many times a main breaker panels are a better value than a main lug anyway. It doesn't matter if you put in a 100 amp main breaker when your are feeding it with say, a 60 amp feed. As long as you protect the feeders with the correct sized breaker, the 100 amp is acting as just a disconnect.
 