12/4 or [email protected]/2

I am putting in a bathroom fan/light/heater on its own 20 amp circuit. I'll be using a switch with a timer plus 2 rockers.

So I'll need 3 hot, 1 neutral, and 1 ground from the switch box to the unit.

I could use 12/4. But would it be ok to use 2 12/2 cables instead?
 
Sponsored Links
  #2  
Old 01-29-09, 02:41 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Didn't know they made 12/4?. So, 3- 12/2's would be the ticket.

Or 1-12/2 and 1-12/3.
 

Last edited by wirenut1110; 01-29-09 at 02:48 PM. Reason: wrong info
  #3  
Old 01-29-09, 04:02 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
Yes they do make 12/4 (black, red, blue, white, ground) but it's probably a special order item. There's also 12/2/2 (black, white, red, red stripe, ground) which you could re-identify red stripe as a hot wire using a Sharpie pen.

If the fan/light/heat fixture has separate neutrals for each function, you could use a 12/2 and a 12/3; or three 12/2. Just be sure to keep the correct switched hot with its matching neutral.

Or you could install some ENT "smurf tube" flexible PVC conduit and pull individual THHN conductors through in appropriate colors. I would probably go this route.
 
  #4  
Old 01-29-09, 04:10 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
For this set up there are two thing you will useally need to do this.,

Get two gang switch box ( minuim size ) { trust me on this one you will have issue with the numbers of conductors }
otherwise 3 gang switch box will have more leeway and room to work around.

you can use 12-2-2 { pretty common item in AFCI required states } or use the 12-4 { you can get it but some place may have specal order for this }

Or

Run with smurf tube { nonmetalic fexiable conduit } and run proper sized THHN/THWN conductors

Myself I rather run the latter if there is no issue bring it in.

Merci,Marc
 
  #5  
Old 01-29-09, 04:13 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
Just checked the catalog. Southwire seems to be the only manufacturer who makes true 12/4 NM-B, but only in 250' rolls and 1000' spools.

Southwire and Cerrowire both make 12/2/2, but again only in 250' and 1000' lengths. The supply house may be willing to sell on a per foot price. Personally, the ENT route sounds easier to deal with.
 
  #6  
Old 01-29-09, 05:06 PM
Member
Join Date: Apr 2007
Location: Near Buffalo, NY
Posts: 4,239
Originally Posted by ibpooks View Post
you could re-identify red stripe as a hot wire using a Sharpie pen.
Just a quick aside, ib ...

I see a lot of installed low-voltage systems that were labeled with Sharpie pens. After a few years the Sharpie ink dries out and disappears off of PVC-jacketed wiring.

As much as I hate electrical tape, this is one time I would use it instead of a Sharpie.

Just sayin' ...
 
  #7  
Old 01-29-09, 09:33 PM
Member
Join Date: Jan 2004
Location: Baltimore
Posts: 1,143
Can someone explain why the posters idea of using 2 12/2 is not ok? Assuming common neutral for all (he said he needed 3 hots, 1 neutral and 1 ground). from first 12/2 use 1 hot, 1 neutral and 1 ground. from second 12/2 use black as hot, relabel white as hot. and I guess you would have to use the ground as well since you can't have conductors without ground, correct? Since it was said he need 3 12/2, I assume you can't relabel the white in this situation. Can someone explain please. thanks.
 
  #8  
Old 01-29-09, 10:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
For any given circuit, the hot, neutral and ground conductors must be in the same raceway. Separate cables are separate raceways.
 
  #9  
Old 01-29-09, 10:16 PM
Member
Join Date: Jan 2004
Location: Baltimore
Posts: 1,143
so the outer jacket counts as raceway? someone said could use (1) 12/2 and (1) 12/3 or (3) 12/2. if doing either of these, I guess you would have to connect all the neutrals together and all the grounds together. I guess that is why easier to use the conduit as you only need one neutral and one ground.
 
  #10  
Old 01-30-09, 08:39 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
Yes, the outer jacket of a cable is a raceway (or at least is treated like one). He can use a 12/2 + 12/3 if the heat, light, and fan functions of the fixture have separate neutrals. He can then match them with the proper switched hot in each cable. In my opinion though, the conduit, 12/4 cable or remarked 12/2/2 cable is the proper way to go.
 
  #11  
Old 01-30-09, 08:13 PM
Member
Thread Starter
Join Date: Feb 2006
Location: TN
Posts: 74
Thanks for the replies. No, there are not separate neutrals. I don't have the switch or unit yet, but I have the wiring diagrams. I guess I'll go the 12/4 or 12/2/2 route if I can get a short length of it, otherwise the conduit.
 
  #12  
Old 02-06-09, 02:01 PM
Member
Thread Starter
Join Date: Feb 2006
Location: TN
Posts: 74
So I went to Home Depot to see if they had 12/4 or 12/2/2/. They didn't, although they had a 12/2/2 sign on their cut by the foot display.
Anyway, their electrical person advised me to use a 12/2 plus a 12/3. But unlike ibpooks says above, there are not separate neutrals, just one. The HD electrician said to tie the two neutrals together. Bad idea?
 
  #13  
Old 02-06-09, 03:39 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,044
While a few HD employees are retired electricians some have at most just a couple of hours training watching a very basic computer based training program. Others may have been to a few manufactures training seminars.
 
  #14  
Old 02-06-09, 05:03 PM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,174
Originally Posted by smalc View Post
The HD electrician said to tie the two neutrals together. Bad idea?
Tieing the neutrals together serves no real purpose, and only adds some confusion and wiring time. NEC 300.3 (3) allows, using NM cable, cable grouping. Basically, run the two NM together for the run, and enter any metal box using the same hole/clamp. 300.20 (A) is referenced also.
 
  #15  
Old 02-06-09, 07:58 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
Originally Posted by smalc View Post
Anyway, their electrical person advised me to use a 12/2 plus a 12/3. But unlike ibpooks says above, there are not separate neutrals, just one. The HD electrician said to tie the two neutrals together. Bad idea?
After this thread popped up last time, one of the other moderators and I had a brief discussion about this topic and decided that you can use 12/2 + 12/3 for this purpose. The code article 300.3 applies as referenced by telecom guy.
 
  #16  
Old 02-07-09, 02:58 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Originally Posted by ibpooks View Post
After this thread popped up last time, one of the other moderators and I had a brief discussion about this topic and decided that you can use 12/2 + 12/3 for this purpose. The code article 300.3 applies as referenced by telecom guy.

It is allowed to do that in few situation it been done like that more than once.

But a nice gotcha as Telecom and Ipbooks and myself I will mention that if you have plastic switchbox then it is not legit at all unless you have NM clamp to keep the NM's bundled as above.

Merci,Marc
 
  #17  
Old 02-07-09, 06:00 AM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Originally Posted by ibpooks View Post
There's also 12/2/2 (black, white, red, red stripe, ground) which you could re-identify red stripe as a hot wire using a Sharpie pen.
Just an FYI but, you can only re-identify a white to feed a switch, not use it as a switch leg.
 
  #18  
Old 02-08-09, 08:53 PM
Member
Thread Starter
Join Date: Feb 2006
Location: TN
Posts: 74
Originally Posted by telecom guy View Post
Tieing the neutrals together serves no real purpose, and only adds some confusion and wiring time. NEC 300.3 (3) allows, using NM cable, cable grouping. Basically, run the two NM together for the run, and enter any metal box using the same hole/clamp. 300.20 (A) is referenced also.
Thanks, what is the reason for the metal box requirement? If the neutrals are not tied together, will I have one loose?
 
  #19  
Old 02-08-09, 08:57 PM
Member
Thread Starter
Join Date: Feb 2006
Location: TN
Posts: 74
Originally Posted by ray2047 View Post
While a few HD employees are retired electricians some have at most just a couple of hours training watching a very basic computer based training program. Others may have been to a few manufactures training seminars.
She wasn't old enough to be retired, but seemed pretty knowledgable. She had wired one of these units before, she said.
 
  #20  
Old 02-09-09, 05:40 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Once you see how small the junction box is on the fan you are going to wonder how to get all of them to fit in there when using multiple cables.

I feel the best approach is to run smurf tube (ENT) or a flex conduit with individual conductors.
 

Last edited by pcboss; 02-09-09 at 07:38 AM.
  #21  
Old 02-09-09, 07:13 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,174
Originally Posted by pcboss View Post
I feel the best approach is to run smurg tube (ENT) or a flex conduit with individual conductors.
This should be the best method. Only one ground wire on each end to deal with, and you can run a red, orange, black for the 3 hots. Only one white. How many total watts?
 
  #22  
Old 02-09-09, 07:38 AM
Member
Thread Starter
Join Date: Feb 2006
Location: TN
Posts: 74
Originally Posted by telecom guy View Post
This should be the best method. Only one ground wire on each end to deal with, and you can run a red, orange, black for the 3 hots. Only one white. How many total watts?
Ok, I am starting to warm up to the ENT approach. What diameter would I need for the 3 hot, 1 neutral, and ground? This will be a dedicated 20 amp circuit.
 
  #23  
Old 02-09-09, 07:42 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Half inch, 1/2" ENT is good for up to 7 #12 THHN conductors.
 
  #24  
Old 02-09-09, 09:12 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,044
Just a suggestion use stranded wire if you go ENT. Easier to work with.
 
  #25  
Old 03-19-13, 12:40 PM
Member
Join Date: Mar 2013
Location: USA
Posts: 9
Other Options

I believe up in northern US/southern Canada area, they sell Romex with a blue sheath. It includes 3 hots, 1 neutral, and 1 ground, as was stated as a requirement. If you can buy this, Then I believe that's the way to go. Beware, however; I believe it only comes in 10 AWG and 8 AWG sizes. You may just want to use the Romex I stated at 10AWG and put it on 20a breakers that are bolted together or tripped at the same time in the event of a short, etc. Tell the inspector that you used 10AWG to compensate for voltage drop. He'll probably take that in and pass it out.
Sparky
 
  #26  
Old 03-19-13, 12:42 PM
Shadeladie's Avatar
Super Moderator
Join Date: Jan 2005
Location: USA
Posts: 3,928
Hello. I'm sure the problem's been taken care of after 4 years.
 
Closed Thread

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes