Jumpering off the load side of a GFCI outlet?

Here is what I want to do in my master bathroom.

I have an existing GFCI outlet that provides protection to that outlet in the master bathroom as well as to a separate outlet the 2nd bathroom. What I want to do is extend the circuit from this outlet to feed a light fixture near the bathtub. I've been informed that the electrical code requires any light fixture within 6 feet of a bathtub or shower to be GCFI protected.

Is it ok to run a pigtail from the load side of the GFCI outlet to a wall switch and then run wire to the light fixture itself? Is this configuration up to code? Is there another way to do this?

-RR
 
Sponsored Links
  #2  
Old 02-11-09, 12:15 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
No, not really, code requires bath receptacles to feed only bath receptacles, not lighting circuits. The only time you put lights on that circuit is if that circuit only feeds that bathroom.
 
  #3  
Old 02-11-09, 04:37 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,949
Received 33 Votes on 28 Posts
Where did you hear about the need for the GFI protection for the lighting?
 
  #4  
Old 02-11-09, 06:05 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Are you in the United States?

For best advice, please fill in the location field of your profile.
 
  #5  
Old 02-12-09, 07:19 AM
Member
Thread Starter
Join Date: May 2008
Location: Northern Virginia
Posts: 4
Received 0 Votes on 0 Posts
My assumption for needing GFI protection for lighting was based upon the review of installation instructions. I have found text similar to this: "If this fixture is located above or near a tub or shower, it must be marked as appropriate for the application and be connected to a GFCI (Ground Fault Circuit Interrupter) protected circuit." I remember this from the last time I replaced a bathroom exhaust fan.

In the current situation, the light fixture would be 3 to 4 feet away from the leading edge of the tub/shower combo.
 
  #6  
Old 02-12-09, 08:12 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,949
Received 33 Votes on 28 Posts
There is no code rule regarding GFI protection for lighting near or over a tub, unless specified in the installation instructions. The fixtures do need to be 'damp rated' over the tub.

You are correct about the exhaust fan requiring GFI protection when over a shower or tub as it is required in the installation instructions.
 
  #7  
Old 02-12-09, 09:31 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Somehow you translated "near" into "6 feet". That translation was unsupported. If the manufacturer did not quantify "near", then I would consider 3 to 4 feet as "not near".

If you do put this on GFCI, you may (or may not) need to use a dead-front GFCI to avoid code issues (depending on what else is on the circuit).
 
  #8  
Old 02-12-09, 09:59 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,949
Received 33 Votes on 28 Posts
Since the circuit serves more than one bathroom adding the lighting load is not Code compliant and should not be added.
 
  #9  
Old 02-12-09, 05:30 PM
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
Code can be kind of interesting sometimes. Hard to figure if they are trying to protect you or not. Or have other more important agendas.

Didn't they consider someone might decide to take a shower (maybe drunk) and change out the lightbulb at the same time -maybe even a broken bulb that needs extraction from socket?

Why have the rule for a bathfan, but not for a light?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: