Panel Wired Correctly

I opened my panel for the first time to install a new breaker and noticed there is no seperate neutral bar. There are 2 bars, 1 on each side connected together. They ran all of the neutral and commons to the same bars since they are all connected. There is also no neutral coming into the box.

I thought it had to have this?

Thanks,
Gates
 
Sponsored Links
  #2  
Old 02-15-09, 06:41 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
In a 3-wire service entrance, that big bare one is your grounded conductor(neutral) then you'll see like a #4 or 6 bare copper wire and that's going to your grounding electrode system.

You're good, don't worry
 
  #3  
Old 02-15-09, 07:07 PM
Member
Thread Starter
Join Date: Feb 2009
Posts: 5
Received 0 Votes on 0 Posts
So just keep placing the neutral and ground on the same bar? I have 3 wires coming in 2 go to the main breaker then an unshielded on going to the bar.
 
  #4  
Old 02-15-09, 07:14 PM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
Received 1 Vote on 1 Post
Yes at the point of the first disconnect (main breaker) grounds and neutrals are bonded together, anything after that they're separated.

It's ok to double on grounds on the bar but don't double up neutrals, and if you do double up on grounds do so with the same size wire.

The bare one is the neutral. After that point, it is insulated.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: